Posted By: sparky02 demand and connected load - 12/05/01 07:52 PM
how do i determine the demand load of a building i.e. a school has a connected load of 299 amps what is the demand load? also does anyone know the maximum open circuit voltage on a dwelling unit? im using a study guide for the contractors exam and the approved reference materias do notseem to have this info in them.
Posted By: Joe Tedesco Re: demand and connected load - 12/05/01 09:50 PM
See Section 220-34 and Table 220-34 and Section 210-6(a)in the 1999 NEC.
See also Section 410-80(b).

[This message has been edited by Joe Tedesco (edited 12-05-2001).]