Posted By: HotLine1 Tester question - 01/24/06 12:54 AM
Guys:

A multi-part quick question.....

Anyone use/have an AFCI Tester???

If so...mfg and model & rough $$$


AFCI's are not required here in NJ, but, one job has them within spec, and I have the inspections upcoming soon

Thanks,

John
Posted By: iwire Re: Tester question - 01/24/06 12:58 AM
John according to UL there is no such thing as an AFCI tester, only AFCI indicators.

Some of these indicators will not trip certain brands of AFCIs.
Posted By: Celtic Re: Tester question - 01/24/06 01:00 AM
How can you put them in when they haven't been accepted by the State?
Posted By: Tiger Re: Tester question - 01/24/06 04:24 AM
Although I have an Ideal tester with a button for AFCIs my understanding is that UL tests and approves them only by pushing the test button on the breaker.

Dave
Posted By: OreElect Re: Tester question - 01/24/06 06:02 AM
http://www.professionalequipment.com/xq/ASP/ProductID.3838/id.5/subID.57/qx/default.htm
Posted By: HotLine1 Re: Tester question - 01/24/06 10:38 PM
Celtic:
They are within the 'specs' for a hotel job in town.
As to NJ, they are not 'required' within the adopted NEC, but they can be installed.

John
Posted By: HotLine1 Re: Tester question - 01/24/06 10:41 PM
OreElect:
Thanks for the link, it's printing now.
I'll give it to the director AM to have a PO cut.

John
Posted By: HotLine1 Re: Tester question - 01/24/06 10:46 PM
Bob:
Thanks for the input. I have a info request into Siemens, and the job EC is hunting also.

Tiger:
Your tester is probably the one in the link provided by OreElect???

Celtic's query regards NJ not adopting the AFCI requirements within '02 & '05 NEC, but I have to inspect based on spec also. This is the 1st AFCI job I have encountered.

John

Thanks guys.
Posted By: LK Re: Tester question - 01/24/06 10:51 PM
Celtic,

We are in New Jersey, and have been installing AFCIs when ever the customer or spec, called for them, we had a few hours of discussion, on this subject at our last CEU class.