what should an amp draw be at start up
on a a/c compressor?
zxone
That would depend on the size of the compressor.
Roger
nominal amps time 6 is minimum for start.
A motors code letter indicates how much kVA per HP with a locked rotor.
See Table 430.7(B).
thank you for the infomation
zxone