Posted By: drgnz23 sub panel - 10/14/05 08:33 PM
Im going crazy! I swore i read something in ECM mag that a sub panel in a detttached garage must have a separate ground rod . Is this true or im i mistaken?
Posted By: iwire Re: sub panel - 10/14/05 08:45 PM
Yes that is correct, take a look at 225.30 through 225.40 for all the requirements that you will need to follow for a detached garage panel.
Posted By: harold endean Re: sub panel - 10/15/05 12:21 PM
Bob,

I read on another web site that it is also useful in case of lightning. You want the lightning to disapate in the earth by the garage in stead of trying to get back to the main house.
Posted By: drgnz23 Re: sub panel - 10/16/05 02:44 AM
Thanks fellas . I knew i read something about that