Posted By: wv-wire-wrangler Class stumped? - 10/05/05 03:31 AM
Hi all,

I just got home from my journeyman class and we were given a practice test that the whole class checked together. One question had an answer that kinda half stumped the class, including the teacher.

Here it is:

Which are the three basic electrical faults?

a) Ground fault, partial ground fault, and open circuit.

b) short circuit, open circuit, and change in electrical value.

c) open circuit, incomplete circuit, and ground fault.

d)short circuit , ground fault, and partial ground fault.

The test writing program the teacher uses said the answer is (D), but what is a partial ground fault? Even our teacher has never heard of one!

Sam

[This message has been edited by wv-wire-wrangler (edited 10-04-2005).]
Posted By: dmattox Re: Class stumped? - 10/05/05 03:39 AM
A partial ground fault would be a fault to ground not at full potential, such as in a motor winding.
Posted By: jw electric Re: Class stumped? - 10/05/05 03:42 AM
Could it be where there is an accident? Some one stepped into a hole in the ground. Would that be a partial ground fault? I mean if the ground didn’t have the hole then the accident would not have happened.

Of course it will be hard to find a lawyer that will try to sue the ground no matter how much it was at fault.
[Linked Image] [Linked Image] [Linked Image]
Posted By: wv-wire-wrangler Re: Class stumped? - 10/05/05 03:48 AM
Hey JW,

GOod one. Had me laughing for a good 5 minutes!!! [Linked Image]
Posted By: gfretwell Re: Class stumped? - 10/05/05 05:32 AM
A partial ground fault is one that trips a GFCI but not the O/C device.
That may be the hardest one to find.
Posted By: IanR Re: Class stumped? - 10/05/05 11:08 AM
I like JW's explanation. However on what grounds(partial grounds?)are you basing that explanation. [Linked Image]
Posted By: WFO Re: Class stumped? - 10/05/05 11:15 AM
Seems like an strange question, since a ground and partial ground fault are both types of short circuits.
A partial ground would probably be a high impedance ground, often one that doesn't pull enough current to activate a protective device (like gfretwell said).
A good example would be high voltage line falling on dry sand. The sand (basically glass) is such a high impedance that the line never trips. That's why you never see a lineman touch a downed wire without grounding it.
Posted By: Ron Re: Class stumped? - 10/05/05 11:35 AM
If it were are fill in the blank question, I would have answered 3 phase fault, line-ground fault and 3 phase arcing fault (high impedance fault)

Other flavors would be line-line fault, line-line arcing fault and line-ground arcing fault.

So maybe according to that author, a partial fault is an arcing fault.
Posted By: George Corron Re: Class stumped? - 10/05/05 11:56 AM
I don't like the question either, BUT....

A partial ground fault is one most often on a high line (distribution or transmission levels) where you have an arc to ground, way to small to cause an interruption current.

What is does cause is RFI, TVI, etc. In Other Words, a ground fault NOT at interruption levels that uses power, and causes customer problems.
Posted By: CTwireman Re: Class stumped? - 10/05/05 02:49 PM
I disagree with this question entirely. There are only 2 basic types of faults, shorts and opens.

You can then get more specific and subdivide both of those categories, such as ground faults, line to line faults, etc.

But "partial ground faults?" That is very vague and confusing in my opinion.

Peter
Posted By: IanR Re: Class stumped? - 10/05/05 03:17 PM
I agrre. The question is so vague it causes more confusion than it teaches. I mean hey it confused a whole class. Sounds more like an author is nitpicking about semantics.
Posted By: IanR Re: Class stumped? - 10/05/05 03:20 PM
Quote
Of course it will be hard to find a lawyer that will try to sue the ground no matter how much it was at fault.

Are you kidding, they sue Jesus himself if they could drag him to court. [Linked Image]



[This message has been edited by IanR (edited 10-05-2005).]
Posted By: pauluk Re: Class stumped? - 10/05/05 04:59 PM
I agree, it's a very unfair question in my mind.

Option D doesn't even cover an open circuit, one of the two basic categories of main faults (shorts and opens).
Posted By: hypress Re: Class stumped? - 10/05/05 10:51 PM
In an ungrounded system you can have verrying degrees of ground faults. When we thump grounds we have a ammeter and the thumper generates a thump in relation to the quality of the ground fault. I have seen 2amp grounds which are hard to find then I have seen 10 amp grounds that are easy to find.
Posted By: hbiss Re: Class stumped? - 10/05/05 11:27 PM
Option D doesn't even cover an open circuit, one of the two basic categories of main faults (shorts and opens).

A fault by definition is any situation where the resistance between the current carrying conductors themselves and/or the neutral and/or ground decreases to where current begins to flow through the resistance. A dead short is one example, a squirrel (also dead) is an example of a partial fault.

Notice that an open would not fall into this definition and should not be referred to as a fault.

Answer "D" is correct.

-Hal
Posted By: frank Re: Class stumped? - 10/06/05 12:23 AM
There are always ground faults according to our LIM's (Line Isolation Monitors)We use them instead of GFCI in operating rooms.Basically they will read from .2 to .8 ma with special silicon gel low leakage appliance cords etc in perfict condition.The LIM will go into warning at 1.5ma and full alarm at 2ma.Dust between the receptacle screws or even wiping down the OR table with a damp cloth will set it off.
I would say partial ground faults are everywhere its just where and what point it becomes a problem.
Posted By: sparky970 Re: Class stumped? - 10/08/05 04:16 PM
WFO hit it right, it has to do with a high impedance grounding system.
Posted By: hbiss Re: Class stumped? - 10/08/05 04:25 PM
it has to do with a high impedance grounding system

No, a high impedance grounding system would not be a fault since it is intended to operate that way.

-Hal
Posted By: WFO Re: Class stumped? - 10/08/05 09:38 PM
Quote:
"No, a high impedance grounding system would not be a fault since it is intended to operate that way."

Re-read my post. I was referring to unintentional grounds; specifically those involving conductors whose current flow is only limited by the impedance of the soil they lay in.

Quote:
"Notice that an open would not fall into this definition and should not be referred to as a fault."

This got me to thinking about the example I referred to above. We once had a 7200 volt line down that didn't trip the breaker in the substation. We put an ammeter in the metering circuit and could not get a descernable reading. So even though the line was physically in contact with the earth, it was technically an open circuit.

A fault or not?

On the other hand, I've seen a damaged underground 240 volt feed to a barn spin the KWH meter like a helicopter, but never trip its' breaker because the earths' impedance kept the current below it's trip point.

So let's look at one other example (just to play devils' advocate). The 240 volt heating element (4500 watt)in a hot water heater loses its insulation at precisely the midway point of the heating element. Since each half of the element is is now at half voltage (120 to ground through the tank) through one half the resistance, the current flow has not changed and the water still heats. Is it a fault?
Posted By: IanR Re: Class stumped? - 10/10/05 01:21 PM
"is it a fault"

Technically yes because the system is not operaring as designed. Additionally now you have a 120 volt load using the EGC as a current return path. But I can almost see what you are getting at.
Posted By: WFO Re: Class stumped? - 10/11/05 02:37 AM
"Technically yes because the system is not operaring as designed."

Bingo! Test questions get a little simplistic.
Posted By: danickstr Re: Class stumped? - 10/11/05 03:26 AM
probably many of you have heard of a water line being corroded away by a trickle charge going out the ground. I wondered what type of fault this would be called in this test.