Posted By: bot540 IMC ? - 09/01/05 02:20 AM
Is IMC made of steel only, or is aluminum, or both? Me and another journeyman had this argument today.
Posted By: Tiger Re: IMC ? - 09/01/05 02:52 AM
Steel with a coating of zinc.

Dave
Posted By: iwire Re: IMC ? - 09/03/05 08:51 AM
You know the code book can solve many disagreements. [Linked Image]

RMC can be, steel, stainless steel, aluminum, silicon bronze.

Quote
344.2 Definition.
Rigid Metal Conduit (RMC). A threadable raceway of circular cross section designed for the physical protection and routing of conductors and cables and for use as an equipment grounding conductor when installed with its integral or associated coupling and appropriate fittings. RMC is generally made of steel (ferrous) with protective coatings or aluminum (nonferrous). Special use types are silicon bronze and stainless steel.

On the other hand IMC is steel.

Quote
342.2 Definition.
Intermediate Metal Conduit (IMC). A steel threadable raceway of circular cross section designed for the physical protection and routing of conductors and cables and for use as an equipment grounding conductor when installed with its integral or associated coupling and appropriate fittings.

[This message has been edited by iwire (edited 09-03-2005).]
© ECN Electrical Forums