Posted By: pauluk Multiple services & Neutral bonding - 11/09/01 11:10 PM
A couple of topics here got me to thinking some more about multiple services to a building.

Suppose you have a commercial building fed with 277/480V Wye. O.K, so perhaps in most cases there would be a customer-owned xfmr to get local 120/208 service, but what if the PoCo provides a separate 120/208V Wye (or a 1-ph 3-w 120/240V supply).

If the NEC requires neutral-ground bonding at each main panel, how does the PoCo feel about having the neutrals of two different services effectively connected together in this way?
Posted By: ElectricAL Re: Multiple services & Neutral bonding - 11/10/01 01:01 AM
In my experience, the power company enforces the grounding of the neutral at the building as part of their pre-energization tests, even when there is no other AHJ. In the un-inspected areas I have experienced, the PoCo lineman will make sure the neutral is bonded to ground before he runs the service lateral. . .anything else may well be ignored, but not that. I take that as evidence that the PoCo is all for the neutral ground bond even when it cross neutrals different systems.

Al
Posted By: sparky Re: Multiple services & Neutral bonding - 11/10/01 02:18 AM
There really cannot be any true N isolation with the N&G practice used here, be it under one roof, or having a common municipal bond.
Posted By: pauluk Re: Multiple services & Neutral bonding - 11/10/01 11:20 AM
Yeah, that's pretty much what I was thinking from the recent posts on this.

I can see more of this discussion arising in the U.K. with the increasing use of PME (i.e. bonded N-G).
Posted By: sparky Re: Multiple services & Neutral bonding - 11/10/01 11:50 AM
There has been, ROP's as i understand, as to a N-G separation back to the serving X-former. The NEC has dictated 'codes' for many other trades, but that seems to stop at the utilities, who seem impenetrable.
Posted By: pauluk Re: Multiple services & Neutral bonding - 11/10/01 05:05 PM
Something like the U.K. system in my diagram #1, you mean? I have to confess that I like that system a lot, although I wouldn't be adverse to installing a ground rod at each house as well, just to be certain.

What's ROP by the way?
Posted By: electure Re: Multiple services & Neutral bonding - 11/10/01 09:52 PM
Way off the subject, but we have a "Regional Occupational Program"(ROP) in the high schools here, which teaches mainly agricultural occupations.
Here in North Orange County, it is abbreviated as NO CROP [Linked Image]
Posted By: sparky Re: Multiple services & Neutral bonding - 11/11/01 01:20 PM
Scott, soundslike a federal program [Linked Image]

Paul; http://www.nfpa.org/Codes/National_Electrical_CodeR__NEC/Proposals/necpdf/A250.PDF
ROP= Report on Proposal, anyone can write and submit one, but it usually needs to be of indisputable quailty to amount to an NEC change.

there are ROC's = Report on comments, where there are some points of views that are , at least in my opinion, real rippers. One individual's letter on the recent change of 'fixture' to 'lumiaire' eluded to plumbers mistakenly mounting toilets on kitchen cielings , absolute 5-star ripper! [Linked Image]
Posted By: Scott35 Re: Multiple services & Neutral bonding - 11/12/01 08:39 PM
Scott [electure],

Haven't heard about NOCROP for years!!! I learned Diesel Mechanics in 1982-3 at Loara High School in a NOCROP program.
Give me a call sometime [Linked Image]

As to this thread;

I have seen a few PoCo supplied systems / services as described. Seems to me that the whole thing would be as any other type of "Dual Services" or even SDS [Separately Derived System] would be - as far as the Grounding / Grounding Electrode System is concerned.

Just my thoughts.