Posted By: bucketman got HDPE? - 06/15/05 06:27 AM
Has any one seen or used "High Density Polyethylene Conduit?
I just came acrost it in the code and know nothing more then that.
Posted By: e57 Re: got HDPE? - 06/15/05 07:11 AM
No....

I had to google. http://www.polieco.com/eng/prodotti_cavidotti.asp

Funny it looks like drain pipe to me....
Posted By: Ryan_J Re: got HDPE? - 06/15/05 12:56 PM
I'll bet you've seen big rolls of it on the back of utility trucks before. Probably blue or red.
Posted By: cpal Re: got HDPE? - 06/15/05 01:34 PM
Carlons web site has pdf info
Posted By: IanR Re: got HDPE? - 06/15/05 01:50 PM
We use it under raised floors in some of our systems we build. While I have not personally worked with it, it seems pretty durable.
Posted By: cpal Re: got HDPE? - 06/15/05 03:17 PM
353.12 appears to limit the use of HDPE to exterior installations only??


Charlie
Posted By: macmikeman Re: got HDPE? - 06/15/05 04:49 PM
We used to use it pretty regularly in residential to provide a chase for tv cable and phone cable to be run underground from the street box to the demark for the house. Both the cable co. and the phone co. now insist on a min 1" pvc conduit for the same job.
Posted By: Ryan_J Re: got HDPE? - 06/15/05 04:57 PM
Please read Charlie's reply again. You cannot use this wiring method at all in the 2002 NEC, and in the 2005 it must be outdoors and concelaed.