Posted By: SJT Transformers - 05/19/05 06:58 PM
We have a 225kva transformer, with 480v primary and 208 sec. The installation the way it is now, has 2 - 4" seal tights, each going to a 400amp switch. Are you allowed 2 diffrent disconnects on the secondary side? Do the secondary conductors have to terminate into a single switch or breaker? Such as a 600 amp main breaker panel? Can they end up into 2 switches?
Thanks
Posted By: Yoopersup Re: Transformers - 05/19/05 08:09 PM
Is this in a Superivised Industrial site or not?? (240.2) definitions.If so read 240.90 if not read 240-21c.
Posted By: SJT Re: Transformers - 05/20/05 06:57 PM
Thanks for the input