Posted By: mhulbert Mounting Lights in Trees - 05/19/05 01:27 AM
I have a customer that would like me to mount some PAR 30 floodlamps in his trees for a horseshoe pit. I have seen this done a number of times, however, I am not sure of the best and most reliable way to do it.

Power is coming up from the ground as 1/2" PVC. I would like to transition to RGC and go up the tree to a WP box, and mount the lights to that. However...how does a tree growing/blowing in the wind affect this??? Where does a tree gain its height?? If it is from the bottom, I think that my plan won't work! Anybody have any ideas on how to aproach this?

Mike
Posted By: dmattox Re: Mounting Lights in Trees - 05/19/05 01:33 AM
I think I remember reading an arcticle about this no longer being legal in the 2002 code. I don't have my code book with me so I can't verify that right now.
Posted By: dmattox Re: Mounting Lights in Trees - 05/19/05 01:37 AM
Found my code book. Its overhead spans that isnt allowed. Lighting is ok. 410.16(h)
Posted By: Tiger Re: Mounting Lights in Trees - 05/19/05 02:12 AM
I did this several years ago with IMC. I bent the pipe to conform with the shape of the tree and held it with straps and screws as I would with any wooden structure.

Trees get wider, growing from the center, and gain height from the top. I'd consider any shifting of the pipe over the years to be a maintenance issue, like mounting to a 4X4 post that will eventually rot.

Something to also consider is the growth of leaves against the bulbs.

Dave
Posted By: dmattox Re: Mounting Lights in Trees - 05/19/05 02:22 AM
Would sealtight be a better choice?
Posted By: e57 Re: Mounting Lights in Trees - 05/19/05 02:26 AM
Didn't think it was allowed, but apparently is...

Quote
225.26 Vegetation as Support.
Vegetation such as trees shall not be used for support of overhead conductor spans.
Where overhead conductor spans are attached to a tree, normal tree growth around the attachment device causes the mounting insulators to break and the conductor insulation to be degraded. The requirement in 225.26 reduces the likelihood of chafing of the conductor insulation and the danger of shock to tree trimmers and tree climbers. The 2002 Code has deleted the exception to 225.26 that appeared in previous editions, and trees are no longer permitted as support of overhead conductor spans, even on a temporary basis. However, outdoor luminaires and associated equipment are permitted by 410.16(H) to be supported by trees. To prevent the chafing damage, conductors are run up the tree from an underground wiring method. See 300.5(D) for protection of conductors.

So what happens when the tree grows, and pulls the whole install apart?
Posted By: dmattox Re: Mounting Lights in Trees - 05/19/05 02:39 AM
If you "snaked" sealtight up the tree it would allow for growth. Though would it be considered protected with all the kids climbing up the tree? [Linked Image]
Posted By: Rich R Re: Mounting Lights in Trees - 05/19/05 05:39 AM
Definitely need some sort of flexible conduit if you want this to last any amount of time, can't beleive it is even legal to install on a tree but I guess it is.

The worst choice would be something like RGC, there is just no give in it. How about a combination of schedule 80 pvc with expansion couplings and sealtight ?

Visiting Disney world, I saw a lot of this type of installation on trees for attractions. ( thats right...I was looking at electrical as I'm standing in line..does'nt everybody ?) They used UF cable though, must have some permission from AHJ I would guess
Posted By: mhulbert Re: Mounting Lights in Trees - 05/19/05 06:02 AM
These are pine trees, they just go straight up, so luckily no kids on them! I tried to convince the guy otherwise, but there are no other places to mount the lights.

I am now leaning in the direction of sealtite up one side, I just hope it holds up to the weather/sun. I'd strap it every 2 feet and leave some slack in everything. Sch80 Pvc might work too, I think I'd use sealtite for a few feet out of the ground, then PVC to the box.

Thank you for the replies, it's given me some stuff to think about. Any other ideas, please post!
Mike
Posted By: Alan Belson Re: Mounting Lights in Trees - 05/19/05 06:52 AM
The core timber of a tree is solid, and on the trunk any point will remain practically constant to ground level. Growth is outwards on the trunk, the diameter increasing each year, up to 3/4" per annum on a pine. Height on a pine is strictly off the growth tip, (sometimes several tips). So the problem is, the tree growth eventually envelops and buries the fixings. Fixings may then eventually present a hazard when the tree is cut for firewood or lumber, as the buried fix may be hit by a chain/bandsaw. So the best fix is to use long stainless large head nails through a reasonable-sized non-corroding fixing plate laid on the bark, which can be dressed back to provide a flat. Now as the tree grows, it will gently pull the nails with it each year, keeping the plate on the surface, yet giving a good fix.
Alan
Posted By: Steve Miller Re: Mounting Lights in Trees - 05/19/05 10:21 AM
Been there done that many times. Here's how we do it (and it seems to work ok. UF to base of tree. PVC (whole stick) from below grade to height of (min) 8'. Straps are put on loosley to allow for tree growth. Either staple or strap to tree and leave a gap to allow for growth. Hang the lights on FS boxes with enough gap to allow for growth. And the most important part is to tell the HO to call you back in max 24 months to adjust the staples/straps/boxes. When you return you simple put in new staples and pull the old or loosen the screws a bit to get them thru the next 2 yrs.
Haven't had a problem except for one HO who didn't call for 4 yrs and the staple cut the wire due to tree growth.
Posted By: Alan Belson Re: Mounting Lights in Trees - 05/19/05 12:00 PM
Steve, that's a better way than nails, thanks for the idea!
Alan