Posted By: Dnkldorf Feeder/Branch circuits - 04/01/05 09:19 PM
Are all circuits leaving a panel board, protected by breakers considered branch circuits only?

Or Feeders also?
Posted By: iwire Re: Feeder/Branch circuits - 04/01/05 09:27 PM
Circuits leaving a panel can be either branch circuits or feeders.

Quote
Branch Circuit. The circuit conductors between the final overcurrent device protecting the circuit and the outlet(s).

Quote
Feeder. All circuit conductors between the service equipment, the source of a separately derived system, or other power supply source and the final branch-circuit overcurrent device.
Posted By: BobH Re: Feeder/Branch circuits - 04/01/05 11:22 PM
So if a main panel houses a 60a breaker feeding a main lug sub, the conductors between the 60a breaker and the sub-panel are feeders.
Posted By: SolarPowered Re: Feeder/Branch circuits - 04/01/05 11:40 PM
But, it's not necessarily a "feeder" for purposes of Table 310.15(B)(6).

YMMV.
Posted By: BobH Re: Feeder/Branch circuits - 04/02/05 12:18 AM
Why would it not necessarily be a feeder? Are you saying it would be a service conductor(s) if this was a separate building? Please elaborate.
Posted By: SolarPowered Re: Feeder/Branch circuits - 04/02/05 12:49 AM
I'll refer you to this discussion about 310:15(B)(6):
https://www.electrical-contractor.net/ubb/Forum2/HTML/001450.html
Posted By: BobH Re: Feeder/Branch circuits - 04/02/05 01:30 AM
Thanks, that was exhausting but I guess I asked for it.