Posted By: e57 Wierd things happening.... - 03/24/05 12:30 AM
Been doing some work on a building for about a year doing odds and ends maint. stuff. For some reason ballasts and lamps are short lived. Lamps (flouresent) last about six months, same for HID. Incandesant either burn out after 3 months, or explode. Ballast seem to last about 6-9 months. Its not every light, but an inordinate amount of them.

Any ideas?

Harmonics? (Neutral = 700Hz - 1.2kHz, 3 phase Y)
Ghost?

Same place has some major equipment, lots of HVAC, motors. 3 elevators, etc. (One elevator has some issues... pulls 650A in-rush, and sounds like the four hoursemen. No-one knows why.)
Posted By: Attic Rat Re: Wierd things happening.... - 03/24/05 01:53 AM
... Job security,don't knock it..!! [Linked Image] [Linked Image]
Russ
Posted By: wa2ise Re: Wierd things happening.... - 03/24/05 03:37 AM
Bad conections on the neutral? If the neutral is bad, some circuits could see excessive voltage, thus blowing out the lights, etc.
Posted By: DougW Re: Wierd things happening.... - 03/25/05 08:57 PM
When in doubt, blame Elvis:

[Linked Image from populus200407.omnis.ch]

Of course, if you went to ULC and got ordainied, you could charge them for an exorcism:

[Linked Image from populus200407.omnis.ch]
Posted By: Trumpy Re: Wierd things happening.... - 03/25/05 09:29 PM
e57,
Hmmm,
Sure sounds like there are some power quality issues at that place.
I'd be checking the Neutral bus for a start.
Failing that, I'd get some sort of a Power Analyser connected to the Mains, to see what is happening.
Doug,
Looks like someone found the smilies webpage OK. [Linked Image] [Linked Image]
Posted By: e57 Re: Wierd things happening.... - 03/25/05 11:02 PM
Trumpy, thats more along the lines of what I want to hear. I have been wanting to do some PQM on this building since I first heard the elevator conduit rattle. Cant get anyone to pay for it though...

I just got done with 2 TI's there, and while there started doing ballast replacemnts for, and around the building. The building was gutted 'bout a year and a half ago, and it seems like anything with a transformer is on its way out. Makes me worry about waranteeing all my work there.

[This message has been edited by e57 (edited 03-25-2005).]
Posted By: Trumpy Re: Wierd things happening.... - 03/25/05 11:35 PM
e57,
Quote
and it seems like anything with a transformer is on its way out
From that statement, I'd say that your problem is more than likely a Harmonic one.
Harmonic currents in a Transformer cause the windings and core to overheat.
What sort of motor controls are used on the Elevators?.
Posted By: e57 Re: Wierd things happening.... - 03/26/05 03:42 AM
Soft start at 650+ amps!

Which is soft enough considering the data for the motor has LRA at 1300.

I had a post about it a while back, and was going to update the info, but cant find it.

Our silly PM is bidding to re-pull the conductors for it, against my advise. (I don't think it will solve anything, I have suggested PQM from the beginning.)Sometimes working for someone else is like wearing hand-cuffs. She thinks I'm a "Negitive Nancy", I think she should lay off the Prozac, and look at things objectively.

Today, I saw an HID fixture drop out as the elevator started! (You know when the elvator starts by the extreme "Short" sound when the conductors rattle in the conduit.) That has some confirmation for me for voltage drop due to waveform distortion. The elevator rep. and contrctor who did the base build have been fighting about it since day one. Mmmmm Politics!

They also have a bid to change out a UPS that hums so loud they can't rent the space near the room it is in.

If it is Harmonics, I just added 100 work stations, lots of flouresant lighting and several large motors to the mix, with my 2 TI's. We have a meter available, but need 3000A CT up-grade for testing this service, money the PM sees no need for.

If its a neutral problem, I think it is in the main, as the problem seems to be building wide, which also puts our work at high risk. PM not interested in spending some time with a thermometer. In fact, not interested in trouble-shooting at all.

Anyway, I should stop, I'm starting to _itch.
Posted By: jkraft Re: Wierd things happening.... - 03/26/05 04:36 PM
Bad conections on the neutral? If the neutral is bad, some circuits could see excessive voltage, thus blowing out the lights, etc.

Would this be an issue in residential as well, where the neutrals are NOT split?

[This message has been edited by jkraft (edited 03-26-2005).]
Posted By: Dave33 Re: Wierd things happening.... - 03/26/05 04:48 PM
Maybe the elevator wire is undersized,also you might try megging the wires
Posted By: e57 Re: Wierd things happening.... - 03/26/05 07:26 PM
Feeder for the elevator megged OK, the rattle is being blamed on lack of triplexed conductors. An opinion I could buy into, although does not explain other problems in the building. I have done simular runs (Not triplexed), with simular operating amperages, but have not had a rattle like this. It takes an awfull lot to get (3)250MCM to jump around like this.

Now a question for those motor experts out there. Wye system - Delta connected 6 wire motor - 3 poles on soft start - 3 poles on contactor. This is a configuration that I have not seen before. I figure the motor could be damaged if the soft-start failed, which it has in the past. Anyone with an opinion on this?
Posted By: Trumpy Re: Wierd things happening.... - 03/26/05 10:33 PM
Mark,
Quote
Wye system - Delta connected 6 wire motor - 3 poles on soft start - 3 poles on contactor. This is a configuration that I have not seen before
Join the club there, mate!.
I've never heard of a set-up like that before.
So I understand the motor is being fed with both the soft starter and the contactor?.
Why isn't the soft-starter alone feeding the motor and the motor configured for Delta with links between the terminals?.
Posted By: e57 Re: Wierd things happening.... - 03/27/05 12:01 AM
It would be simular to this (see link: delta run diagram), but 1,2,3 on soft starter, and 4,5,6 on contactor, they are linked parrallelon the line side of each, comprising Delta[/].
http://www.usmotors.com/Connections/11658.pdf

I had questioned that the motor might be wired wrong, and was meant to be wye start, delta run, or vise-versa, but the equipment is wired according to manufacturers diagram. As what I guess one would call "Accross the line start, but half soft-start, or delta part start"? It doesn't make a whole lot of sense to me.

This is [i]"Elevator equipment"
, so I really cant mess with it, ie different license, and liability, blah, blah, blah. But it would be interesting to see if this would work better as wye-start/delta-run.
Posted By: bigrockk Re: Wierd things happening.... - 03/27/05 12:03 AM
I think this link might be helpful as far as the motor connections to the soft start are concerned. The soft start is connected exactly as you have described.
http://www.elevatordrives.com/resources/hpv100_techmanual_tm5590.pdf
Posted By: winnie Re: Wierd things happening.... - 03/27/05 12:47 AM
The unit that Bigrockk links to makes perfect sense. You have a thyristor soft start system that reduces the voltage to the motor, backed up with a contactor. The only thing 'strange' about it is that the control circuitry is _inside_ the delta. If either the soft start or the contactor is open circuit, then no current can flow.

I hedge a guess that one of the phases in the motor is reversed, or that a coil or phase group inside the motor is reversed. When a three phase motor is properly connected, you end up with three nodes that can be connected to your three supply leads. Swap any two, and you reverse the motor. But with more than three leads, you can easily reverse _subsets_ of the winding. Most of the motor is pulling in one direction, but parts of the motor are pulling in the opposite direction.

-Jon
Posted By: e57 Re: Wierd things happening.... - 03/27/05 08:07 AM
Bigrockk, yep thats it! Slightly larger for a 75HP motor. I haven't seen a set up like it before.

Jon, I suspected that at first too, but all of the leads go to the right phases, as they are marked.... I cant ring them out as I technically cant touch the equipment. But I did look! One of the i' ans t's I have crossed and dotted. I still have a few more to cross and dot, like I think the pump valve timing is off, and I really what to see what this beast does to voltage elsewhere in the building, crack open the main and check it too.

I'm one of those types of people that have to put both hands on a problem, not just a finger. There is one or a few things wrong there in that building, and just cant get my mind off them.
Posted By: Trumpy Re: Wierd things happening.... - 03/27/05 08:33 AM
Good point Jon (Winnie),
Our motors as they are wound here come out to 6 terminals labelled A1-A2, B1-B2, C1-C2.
A1-A2 constitutes a single winding in a 3-Phase motor, as does B1-B2 and so forth.
You can configure a motor to work in Star or Delta by changing the links within the terminal box or leave the whole thing open with 6 wires fed from a Star-delta Starter.
All of the Star-Delta conversion happens within the Starter itself, with the 3 contactors, 1 Main, 1 Delta and a Star contactor.
There is also (or should be) a timer that changes the Starting Contactor from the Star start to the Delta run mode.
Posted By: bigrockk Re: Wierd things happening.... - 03/27/05 02:56 PM
This is probably a silly question but have you been able to load test the motor? I know you can't touch the equipment but I wonder if using a "clamp on" to test current draw is considered acceptable?
As I am sure you know if all three phases are balanced then it would be a pretty good assumption that the connections (internally and externally) are ok.
Is it possible that the soft starter is not adjusted correctly? Maybe adjusting the soft start to ramp up the voltage a little slower will solve some of the problems such as the rattle in the conduit and Hid lights dropping out when the motor starts.
It has to be tough when you can't really lay your hands on the elevator equipment...the temptation to dig in and solve this would be a little nerve racking.
Posted By: e57 Re: Wierd things happening.... - 03/27/05 06:01 PM
Next time I get access to the equipment I want to get the starter data to compare.

This is the motor data: http://www.markhellerelectric.com/motordata.htm

In-rush is roughly 650+A, with possible larger spikes that I cant see. (About 10 seconds at start, and is the source of the rattle and VD at the disco is 185V from 208V a little too much IMO) operating amperage is roughly 160A - 180A (which I think is high, seeing that the elevator was empty)

I checked VD at start-up of this elevator at my TI panels, which go out of a different section of the same main, and they only drop 1 volt. Not that it doesn't mean there is not other distortions.