I installed a !0 k Koler gen set
last summer W/ an auto transfer switch
did a bunch of them before y2k hit
now the homeowner called me and asked why her
power bill doubled ??????????????
when i did it I tourqed all the line and load lugs
so i'm perplexed where the blead off is coming from.
or is she just useing more power
Thankx
Posted By: DougW Re: Standby generator problem - 01/27/05 11:42 PM
Make sure her $/KwH rate hasn't changed... a lot of folks don't know enough to compare current rate to old ones.
Posted By: rhiphi Re: Standby generator problem - 02/26/05 03:45 AM
Kw /h not changed any other Ideas
Posted By: bentruler Re: Standby generator problem - 02/26/05 04:17 AM
Dying heat pump or water heater?
Posted By: harold endean Re: Standby generator problem - 02/26/05 12:21 PM
I was once called out on a job like that. HO couldn't figure out why the bill was so high. I Checked all around and while I was in basement, I heard something running. Long story short, her well developed a leak in it. The water kept running from the bottom of the well to the top of the well, while never leaving the well casing and the well motor was running for a few days constantly.
Also ask HO if the bought a new self cleaning oven or refrig. there are heaters on the frig to de-ice them. Another point would be if they have elec. water heater. Did they change the temp of the water? Good Luck.
Posted By: harold endean Re: Standby generator problem - 02/26/05 12:22 PM
Another thought, You can check each branch circuit with a clamp on amp meter to see which circuit is drawing the most power. See what is on that circuit.