Posted By: BigB Temperature ratings of circuit breakers - 01/11/05 04:35 AM
I was under the impression all wiring device terminations (including circuit breakers) with ratings under 100 Amps must be treated as 60C terminals unless otherwise marked. I am looking at Spa instructions which call for a 50 amp circuit using #8 THHN/THWN. Using the 60C column only allows for 40 Amps. Are the instructions wrong or is it me?
BigB...maybe 430.53(C)applies to your installation?

shortcircuit
Posted By: iwire Re: Temperature ratings of circuit breakers - 01/12/05 11:11 AM
Big B you are remebering only part of the code section. [Linked Image]

Part of 110.14(C)(1)
Quote
(1) Equipment Provisions. The determination of termination provisions of equipment shall be based on 110.14(C)(1)(a) or (C)(1)(b). Unless the equipment is listed and marked otherwise, conductor ampacities used in determining equipment termination provisions shall be based on Table 310.16 as appropriately modified by 310.15(B)(1) through (6).
(a) Termination provisions of equipment for circuits rated 100 amperes or less, or marked for 14 AWG through 1 AWG conductors, shall be used only for one of the following:

(1)Conductors rated 60°C (140°F)

(2)Conductors with higher temperature ratings, provided the ampacity of such conductors is determined based on the 60°C (140°F) ampacity of the conductor size used

(3)Conductors with higher temperature ratings if the equipment is listed and identified for use with such conductors

(4)For motors marked with design letters B, C, D, or E, conductors having an insulation rating of 75°C (167°F) or higher shall be permitted to be used provided the ampacity of such conductors does not exceed the 75°C (167°F) ampacity.


Look at your breakers, I would bet they are marked 60/75 C or just 75 C

[This message has been edited by iwire (edited 01-12-2005).]
Posted By: BigB Re: Temperature ratings of circuit breakers - 01/13/05 03:24 AM
That's just it iwire, the breaker offers no help. It is a GE THQL 2 pole 50 amp. There is a circle on it with "40C" printed inside the circle, which I think must indicate the ambient temperature it is calibrated at. I tried to research breaker specs but couldn't come up with the info.
Posted By: BigB Re: Temperature ratings of circuit breakers - 01/13/05 03:38 AM
OK I just went out to my truck and examined a bunch of breakers and sure enough, they do say 60/75C on most all of them. I had to get out a magnifying glass for some. I don't have that GE here, I wonder if I just didn't see the fine print.
Posted By: iwire Re: Temperature ratings of circuit breakers - 01/13/05 10:20 AM
Quote
I had to get out a magnifying glass for some.

That and good lighting...it is frustrating to find the markings on some equipment. [Linked Image]

Bob
If I wire a 12kw range in a dwelling with 8-3 copper romex and it hooks up to a 50 amp breaker...how is this OK if the copper wire amperage is 40 amps based on the 60C column?

shortcircuit
Posted By: iwire Re: Temperature ratings of circuit breakers - 01/13/05 11:39 AM
Big B said

Quote
#8 THHN/THWN

Which makes me think he is running a raceway so the 75 C rating could apply.

If it is NM then you are stuck with the 60 C rating.
But romex comes with 90C rated conductors.This is confusing me here.Help me out?

shortcircuit
Posted By: sabrown Re: Temperature ratings of circuit breakers - 01/13/05 03:26 PM
Look in 334.80 Ampacity. Ampacity of NM type cables shall be 60 degree with the 90 degree rating allowed for derating purposes.

Shane
Posted By: Roger Re: Temperature ratings of circuit breakers - 01/13/05 05:06 PM
Shortcircuit, Shane is correct.

Go to this Southwire page and scroll dow to NM-B for an explanation.

Roger
Its been so long since I learned why I run #8 romex to ranges that I forgot about 220.19

The demand factor of 1 range of 12kw is 8kw and thats why I run #8 to my ranges.Which code rule allows that #8 to be on a 50 amp breaker?

shortcircuit
Posted By: iwire Re: Temperature ratings of circuit breakers - 01/13/05 09:25 PM
I do not understand.

Quote
Which code rule allows that #8 to be on a 50 amp breaker?

310.16 rates 8 AWG copper 50 amps at 75 C

As long as we are not using NM and the wire, breaker and other terminals are all 75 C listed we can use a 50 amp breaker with 8 AWG copper.

NM is different regardless of the THHN inside it.

Quote
334.80 Ampacity.
The ampacity of Types NM, NMC, and NMS cable shall be determined in accordance with 310.15. The ampacity shall be in accordance with the 60°C (140°F) conductor temperature rating. The 90°C (194°F) rating shall be permitted to be used for ampacity derating purposes, provided the final derated ampacity does not exceed that for a 60°C (140°F) rated conductor. The ampacity of Types NM, NMC, and NMS cable installed in cable tray shall be determined in accordance with 392.11.
iwire...every freestanding range I've wired for the last 25 years has been wired with # 6 aluminum or # 8 copper connected to a 50 amp breaker.Thats what I was taught to use and thats the way I see electric ranges connected.I used to use #6 SEU until we had to use 4 wire and then I switched to 8-3 romex and I have never been sited for a violation.?

shortcircuit
Posted By: Roger Re: Temperature ratings of circuit breakers - 01/14/05 01:27 AM
Shortcircuit, in the case of "I used to use #6 SEU (AL per above) until we had to use 4 wire and then I switched to 8-3 romex and I have never been cited for a violation". The inspectors simply have not spotted the violation.

Inspectors are like Inspectees, they both make mistakes. [Linked Image]

Roger

[This message has been edited by Roger (edited 01-13-2005).]
So 8-3 romex protected with a 50 Amp breaker for a Range (up to 12KW) is a violation, but can you wire the range with 8-3 romex and use a 40Amp braeaker per Table 220.19 Note 4:
----------------
Table 220.19 Note 4. Branch-Circuit Load. It shall be permissible to compute the branch circuit load for one range in accordance with Table 220.19.
-----------------
Per Table 220.19 Column C:
compute branch circuit load at 8KW
8KW/220V=36.33Amps
8-3 romex with 40Amp breaker OK?
Iwire,Electric Ian,

A quote from the 2002 Massachusetts Electric code:

"334.80. Revise to read as follows:

334.80 Ampacity. Type NM, NMC, and NMS cable shall have conductors rated at 90C(194F). Where installed in thermal insulation, the ampacity of conductors shall be that of 60C(140F) conductors. The ampacity of Types NM, NMC,and NMS cable installed in cable trayshall be determined in accordance with 392.11."

This revision seems to allow #8-3 copper romex to be protected by a 50 amp breaker where the wire isn't installed in insulation...here in Massachusetts.

shortcircuit
Posted By: iwire Re: Temperature ratings of circuit breakers - 01/15/05 10:17 AM
I agree and that is a good point for us MA folks.

Bob
Posted By: George Re: Temperature ratings of circuit breakers - 01/15/05 05:19 PM
shortcircuit ---

It is not clear if the ampacity is before or after final derating.

The intent of the code could be to derate from the 60 degree colume within insulated walls.
George...It is my understanding, for derating purposes the 90C column is used.A 8-3 romex cable run by itself needs no derating.

I interpet the MA code (334.80) that I posted to mean if the 8-3 copper romex I run in a dwelling is imbeded in thermal insulation that I must use the 60C column which restricts the wire to 40amps.

If the wire is run through the basement(which most houses in New England have)along the sill and up through the floor to the freestanding range, NOT imbeded in thermal insulation, then the wire will be good for 50 amps as listed in the 75C column in 310.16

Also take note of the temperature correction factor table below 310.16. If the wire is run in the basement where the average tempature will be 70F-77F or lower around here, I can apply a correction factor of 1.05...or 50amps x 1.05= 52.5amps

On the other hand if the wire is run up through the ceiling embeded in thermal insulation exposed to attic tempatures in excess of (lets say) 114F-122F, then I would figure the amperage of that #8 copper romex from the 60C column with a tempature correction factor of .58...40amps x .58= 23.2 amps.

Quite a swing in allowable ampacity [Linked Image]

shortcircuit