Grounding/Bonding side by side services - 12/03/04 04:15 AM
Due to the high cost of dual meter packs I would like to use two side by side 100 amp meter combos for a two family complex. The dwellings are separate buildings, the service is overhead, and it is not feasable to put a service on each building. Both services will be on one dwelling, with an underground feed to a subpanel at the second dwelling.
To anyone who has done this, how did you set up the grounding electrode system. Will I need 2 rods for each service? I am thinking I can leave panel 1 with my GEC, hit the water and gas, hit the two rods then back up into panel 2.
To anyone who has done this, how did you set up the grounding electrode system. Will I need 2 rods for each service? I am thinking I can leave panel 1 with my GEC, hit the water and gas, hit the two rods then back up into panel 2.