Posted By: hypress Residential Service in Conduit Bonding - 09/24/04 03:21 AM
What is the proper way to bond a residential service entrance installed in conduit? power The power co supplies a meter base with a bonded neutral so if you install the main bonding jumper in the panel that would make the conduit between the panel and meter base in parallel with the neutral and a current carrying conductor.If you use bonding bushings it does the same thing . Just what do you do. THANKS HYPRESS
Some, (myself included) use PVC where possible. This eliminates the parallel path.
Posted By: Ryan_J Re: Residential Service in Conduit Bonding - 09/24/04 01:31 PM
You're exactly right about the parrallel, but theres nothing else you can do. 250.24 and 250.28 tell us to do exactly what you are describing.