Posted By: electricman2 Tapping NM - 08/10/04 12:08 AM
I have to tap a circuit using 12-2NM. The cable runs across ceiling joists and goes down into stud walls at both ends. The run is straight with no slack. I know I can use 2 j-boxes to do this, but does anyone know a better way. Is there a UL listed "flying tap" [Linked Image]
Posted By: iwire Re: Tapping NM - 08/10/04 12:46 AM
Never used them, do not know what they cost but they are made.

[Linked Image from molex.com]

Quote
Tap Connectors


The SC Tap Splice is used for splicing into an existing solid conductor 14/2 and 12/2 cable with ground. Stranded wire versions are available for 16/2, 14/2, and 12/2 wire. This provides the user the ability to add an additional branch line or add modular hookups in their products anywhere they are needed. The Molex Tap Splice is relatively small and fits into walls, floors, and ceiling cavities with ease. Once the Tap connector has been spliced into the cable, the branch line wire to a SC Power Splice Connector can be mated to the Tap.

www.molex.com

[This message has been edited by iwire (edited 08-09-2004).]
Posted By: CTwireman Re: Tapping NM - 08/10/04 01:14 AM
A similar product to what Bob has shown is made by AMP. A simple inline tap costs around $3 wholesale. I have not used them either but I have spoke to people that have and apparently they are good.

Peter
Posted By: Haligan Re: Tapping NM - 08/11/04 01:35 AM
I must be misreading this. Where in electricman's run would this tap splice doohickey go?
Posted By: shortcircuit Re: Tapping NM - 08/11/04 09:43 PM
Is this type of tap connector permitted to be buried in a wall, ceiling, etc...or must it be left accessible for servicing as a juction box would?
Posted By: cpal Re: Tapping NM - 08/11/04 10:14 PM
Amp has a product that will splice or in line tap NM BUT I'M PREETY SURE IT IS ONLY LISTED FOR MOBILE HOMES see this page http://catalog.tycoelectronics.com/...3&RQS=C~11621^P~52148^M~PROP^N~2^G~G
It mentions compliance with articles 545,550,and 551. I have a cut from the manufacture at work and as I recall it has limited uses. We originally looked into the AMP item regarding manufactured homes and connecting the branch runs when the modules where slid together.


IWIRE do you know what the listing restrictions are on the product you posted it would be nice to know if it is acceptable in all occupancies.

Charlie



[This message has been edited by cpal (edited 08-11-2004).]
Posted By: Joe Tedesco Re: Tapping NM - 08/12/04 01:13 AM
545.13 Component Interconnections.

This section covers their permitted use in a special occupancy for Manufactured Buildings only.
Posted By: iwire Re: Tapping NM - 08/12/04 07:22 AM
Joe as these connectors are covered in 334.40(B) wouldn't they be allowable for all occupancy's that NM is allowed?

If not what section prohibits using these in standard dwelling units?

The 2003 UL white book section NONMETALLIC-SHEATHED CABLE INTERCONNECTORS (QAAV)references 1999 NEC Section 336.21 and Articles 545, 550 and 551.

336.21 is now 334.40(B)

Bob

[This message has been edited by iwire (edited 08-12-2004).]
Posted By: Joe Tedesco Re: Tapping NM - 08/12/04 11:24 AM
Bob:

See 300.15 Boxes, Conduit Bodies, or Fittings — Where Required.

A box shall be installed at each outlet and switch point for concealed knob-and-tube wiring.

Fittings and connectors shall be used only with the specific wiring methods for which they are designed and listed.

Where the wiring method is conduit, tubing, Type AC cable, Type MC cable, Type MI cable, nonmetallic-sheathed cable, or other cables, a box or conduit body complying with Article 314 shall be installed at each conductor splice point, outlet point, switch point, junction point, termination point, or pull point, unless otherwise permitted in 300.15(A) through (M).

For a "Boxless Device" See also:

(E) Integral Enclosure. A wiring device with integral enclosure identified for the use, having brackets that securely fasten the device to walls or ceilings of conventional on-site frame construction, for use with nonmetallic-sheathed cable, shall be permitted in lieu of a box or conduit body.

FPN: See 334.30(C); 545.10; 550.15(I), 551.47(E), Exception No. 1; and 552.48(E), Exception No. 1.

NECH:

Structural components or modules are usually constructed in manufacturing facilities and then transported over the road to a building site for complete assembly of a structure, such as a dwelling unit, motel, or office building.

At the on-site location, approved wiring methods are used to interconnect two or more modules.

Exhibit 545.1 shows a type of nonmetallic-sheathed cable connector permitted for such interconnections.

Exhibit 545.1 A type of nonmetallic-sheathed cable connector used for interconnecting modules in a manufacturing building. (Courtesy of Pass & Seymour/Legrand®)

Courtesy: www.nfpa.org




[This message has been edited by Joe Tedesco (edited 08-12-2004).]
Posted By: iwire Re: Tapping NM - 08/12/04 07:56 PM
Hi Joe, thanks for the answer but I am still uncertain on this, doesn't 334.40(B)modify 300.15?

Quote
334.40(B)Devices of Insulating Material.
Switch, outlet, and tap devices of insulating material shall be permitted to be used without boxes in exposed cable wiring and for rewiring in existing buildings where the cable is concealed and fished. Openings in such devices shall form a close fit around the outer covering of the cable, and the device shall fully enclose the part of the cable from which any part of the covering has been removed. Where connections to conductors are by binding-screw terminals, there shall be available as many terminals as conductors.

If this does not modify the requirements of 300.15 what is this sections purpose?

Bob [Linked Image]

[This message has been edited by iwire (edited 08-12-2004).]
Posted By: Joe Tedesco Re: Tapping NM - 08/13/04 02:53 AM
Bob:

The switch, outlet, and tap devices of insulating material that are permitted to be used without boxes in exposed cable wiring and for rewiring in existing buildings where the cable is concealed, etc., it not referring to the product that is used in the 545, etc., areas.

I searched my image library, and could not find the tap devices mentioned, but I am positive that they are the type that we can still purchase that are usually made of brown plastic with the receptacles and or switch all in one enclosure sort of like an in line switch used in the cord on a table lamp.

I can see where the words can be misinterpreted.

Besides that rule was in the code long before the 545 stuff came about.
Posted By: iwire Re: Tapping NM - 08/13/04 08:39 AM
The 2003 UL white book section for these interconnects (QAAV) directly references 99 NEC 336.21 [now 334.40(B)]
Posted By: iwire Re: Tapping NM - 08/13/04 08:49 AM
2003 UL White Book Page 79 (QAAV)
Quote
This category covers self-contained interconnectors employing pressure cable connectors, insulation displacement or insulation piercing connectors for splicing or tapping nonmetallic (NM) sheathed cable.

These interconnectors are intended for installation in accordance with Section 336.21 and Articles 545, 550 and 551 of NFPA 70, ‘‘National Electrical Code.’’

These devices have been evaluated for equivalency to Type NM cable in insulation and temperature rise, and for capability to withstand fault currents, vibration and mechanical shock that may occur during transport of the units in which they are used.
Posted By: Joe Tedesco Re: Tapping NM - 08/13/04 10:42 AM
Bob:

I found the image that describes the devices mentioned in Article 336.

Quote
334.40(B)Devices of Insulating Material.

Switch, outlet, and tap devices of insulating material shall be permitted to be used without boxes in exposed cable wiring and for rewiring in existing buildings where the cable is concealed and fished.

Openings in such devices shall form a close fit around the outer covering of the cable, and the device shall fully enclose the part of the cable from which any part of the covering has been removed.

Where connections to conductors are by binding-screw terminals, there shall be available as many terminals as conductors.

[Linked Image from joetedesco.com]
Posted By: iwire Re: Tapping NM - 08/15/04 11:46 AM
Joe you seem to be ignoring the fact that the UL book section for the tapping connector I posted references 334.40(B) that makes them one and the same.

Different looking devices but covered by the same requirement, no?

Maybe UL is recognizing more products under that section then they used to.

Looking at it from another direction.

If these are suitable NM taps in a manufactured home how can it be said they are unsafe or unsuitable for stick built homes?

This is all academic as I will probably never use these connectors. [Linked Image]

I do use Re-Locs on MC cable and it seems to me that these are nothing different then re-locs for NM cable.
Posted By: Creighton Re: Tapping NM - 08/15/04 03:42 PM
The surface devices pictured have been recognized in the NEC since at least 1940, Sec. 3369. In 1951 the new phrase " - - in existing buildings where the cable is concealed and fished- - " was added, with no record of the proposer or the reason. My opinion is that this splicing device may be OK for manufactured homes and mobile homes, but there is no place for it in normal wiring. How UL listed this is a mystery to me. Creighton
Posted By: iwire Re: Tapping NM - 08/15/04 03:57 PM
Creighton thanks for jumping in on this and please anyone else please jump in too.

I do want to ask about this.

Quote
this splicing device may be OK for manufactured homes and mobile homes, but there is no place for it in normal wiring.

What is the difference, do manufactured homes deserve a lower level of safety?

NM is NM no matter how or where the dwelling is built.

Bob
Posted By: cpal Re: Tapping NM - 08/15/04 06:23 PM
I have been following this post on the side but I would like to re- introduce the question regarding the manufactures installation instructions. Are these things only listed for modular and or manufactured homes????

The Handbook features a P & S Legrand series connector that I have not been able to locate on web, I have visited the MOLEX site posted by IWIRE and they only refer to articles 550 and 551, although some of the text would lead you to believe the product is suitable for all installations. The language in 334.40 (B) as well as 300.15 appears to be permissive, but I would like to see a manufacture actually list the product for a stick built structure.

As I mentioned when I previously investigated this type of product the manufactures’ literature pretty much limited its use to article 550 and 551 installations.

I’m also concerned regarding unrestricted use of this product if it is so difficult to locate in a supply house or a Mfg.Web sites. UL’s white book is generally generic to a product and relies on the manufactures product markings to indicate the suitability of similar designed devices.

Well I guess I would like to see a more definitive listing to insure this product is acceptable in all occupancies.

Charlie
Posted By: BigB Re: Tapping NM - 08/16/04 02:11 AM
In case no one noticed on page 34 of this months EC&M issue there is a description of the device made by AMP. It states "approved for use in a variety of applications, including residential branch circuits, manufactured housing, and pre fabricated building structures." Since manufactured housing and pre fab is mentioned in addition to "residential" this indicates to me they are approved for use in a stick dwelling.
BigB

[This message has been edited by BigB (edited 08-15-2004).]
Posted By: sparkystudent Re: Tapping NM - 08/16/04 05:39 AM
these taps and connectors are the ones i was referring to in another forum thread that was some pictures posted of a house with duck taped blocks in the crawl space. the company i work for uses them in emergency type repairs for nm in walls and in attic spaces. there is a manufactured houseing site near us and we do a lot of the hookups when they slide the 2 halves together aswell as setting the services to them. the literature provided by the wholesale house at the time is that they were suitable for use in the walls and in the attic (listed and labeled for nm, as nmwire is to be used fished in voids ETC.)the company policy is use them only as a last last resort but we have used them, they are easy to get but they are spendy about 3-4 dollars
Posted By: OreElect Re: Tapping NM - 08/16/04 06:02 AM
I went on a service call for no power to a moba home.
Custumer said he was outside when his wife reset the circuit breaker,which tripped every now and then,noticed a flash each time at the foundation vent.
It was one of those #$@!^%$ connector!!
The thing failed and each time they had reset it,it started a small fire and burned itself out. Very bad idea to use these.My opinion.

These remind me of those multi splice things some guy showed a few months ago for doing fast wiring. a real joke.

my 2 cents