Posted By: sparky*62 okay? - 05/28/04 03:49 AM
I want to tap off an existing welder outlet,that is not used and feed a 20 a 2p breaker that will feed an A/C unit. Is it legal? The breaker will be in a small QO panel.
Posted By: Electric Eagle Re: okay? - 05/28/04 11:34 AM
If the conductors are sized properly and you use some type of switch/disco that will allow only one to be on at the same time, it is OK.