Posted By: wiremann-54270 Knob and Tube Wiring - 05/10/04 05:30 PM
I have to enclose some open air splices in knob and tube wiring that ties to romex.
I will be going to look at it tomorrow, but I need some ideas how to get the old stuff into a j-box. Usually k and t is ripped out and replaced, but these people are selling and do not want to spend much.
Posted By: HotLine1 Re: Knob and Tube Wiring - 05/10/04 06:17 PM
Each conductor must enter through an individual KO, and be protected by a non-conductive sleeve and the sleeve should be clamped/secured to the box.

Some people use a grommet in a 1/2" KO, as the 'sleeving', more than likely is unavailable.

Speak to your local AHJ for his/her take on this method.

John
Posted By: Electric Eagle Re: Knob and Tube Wiring - 05/10/04 11:05 PM
I haven't seen the splices, but if they are original to the wiring, I think they are safer if left alone. I personally would refuse the job if the customer wouldn't allow a rewire of the circuit. Make sure your liability policy is in good order.
Posted By: ElectricAL Re: Knob and Tube Wiring - 05/11/04 03:04 PM
The other side of the coin. . .

Extensions from an existing K&T branch circuit have a history of being normal wiring practice. Depending on local ordinance, they may still be legal to create. The NEC still describes how to do it without a j-box.

300.16 includes "fitting" as well as "box". If the open air splice you are looking at has a "monkey face" transition fitting on the end of the NM cable sheath, then the splices to the existing K&T are permitted without a box exclosing them.
Posted By: HotLine1 Re: Knob and Tube Wiring - 05/12/04 12:02 AM
ElectricAl:
Now there's a fitting name I have not heard of in many years..(Monkeyface)

Back in the 'prentice days we ran accross a lot of K&T, but now it's pretty 'rare' around here. I think the old sleeving is hard to come by, but the monkeyface??? Maybe antique roadshow!

John
Posted By: harold endean Re: Knob and Tube Wiring - 05/12/04 01:13 AM
I should use a plastic box for the K&T otherwise you might have to cut a slot in the metal box if the 2 wires go through different openings.
Posted By: ElectricAL Re: Knob and Tube Wiring - 05/12/04 03:07 AM
John,

I haven't seen a real monkeyface for sale in a very long time, either. This image shows one that terminates the armor sheath on BX cable. [Linked Image]
The basic function is that of a weatherhead, that is, end the raceway or cable and let the individual conductors run on in open air.

If one were to transition now from NM to K&T, using contemporary material, I'd suggest using a threaded ½" weatherhead with a ½" threaded romex clamp.

Al
Posted By: winnie Re: Knob and Tube Wiring - 05/12/04 11:13 AM
I do not know if the below stuff is _listed_ for the application, though the catalog claims 'UL recognized', which I belive applies to components going into apparatus as opposed to finished products. Is this stuff be suitable as the 'sleeving' described? If so, it is pretty easy to get. We use it in our lab for low voltage motor terminations.

McMaster-Carr electrical sleeving catalog page

-Jon
Posted By: ElectricAL Re: Knob and Tube Wiring - 05/12/04 02:03 PM
Over at EC&M, there is a question and answer about this very topic. It is from 2001 and is under the 1999 NEC, but the answer is still accurate, although the code citation numbers shifted some under the 2002 NEC. The NM to K&T splice is the third question, the question at the bottom of the page.
Posted By: Joe Tedesco Re: Knob and Tube Wiring - 05/12/04 08:53 PM
winnie, looks like they may:

UL Lists this product:

[quote}TUBING, FLEXIBLE NONMETALLIC
(YCTR)
These listings include woven flexible nonmetallic tubing (fiber loom) in
trade sizes 7/32 to 2-1/2 in. incl. for installation as mechanical protection
in accordance with Articles 320 and 324 of the National Electrical Code.
The basic standard used to investigate products in this category isUL3,
‘‘Flexible Nonmetallic Tubing’’.
The Listing Mark of Underwriters Laboratories Inc. on the product is the
only method provided by UL to identify products manufactured under its
Listing and Follow-Up Service. The Listing Mark for these products
includes the UL symbol (as illustrated in the Introduction of this Directory)
together with the word "LISTED," a control number, and the product
name "Nonmetallic Flexible Tubing".[/quote]
Posted By: Kobuchi Re: Knob and Tube Wiring - 05/13/04 07:22 PM
I use sleeves (as in the original work) and avoided putting any tight bends on the brittle insulation or using boxes with spring tabs. A clamp that relies on digging-in to sheathing is no good here.

Sometimes those white wires got shared around as common grounds, so do check before you treat them as discrete neutrals.

Yesterday I finished rewiring half a house this way - hopefully the rest will get done during a future reno. So do a favour to the next decade when someone opens your box to complete the job!