ECN Forum
Posted By: Redsy Rooftop unit follow-up - 04/08/04 12:03 PM
Is it OK to mount the disconnect on the rooftop unit? I think it is a bad idea, even if permissible. But, there is no existing mounting rack on the roof, and fabricating one would mean securing it to the roof, which would potentially cause leaks in the future.

Thanks,

John
Posted By: Bomzin Re: Rooftop unit follow-up - 04/08/04 01:07 PM
Yes it's ok, usually mounted right on the unit itself. Why would it be a bad idea, worse idea not to have one.

Bomzin
Posted By: Mean Gene Re: Rooftop unit follow-up - 04/08/04 02:49 PM
I think John's reasoning for it not being a good idea is in the event the chassis of the unit were to become energized or the unit were to catch fire the disco may become untouchable.
Posted By: Anonymous Re: Rooftop unit follow-up - 04/08/04 03:11 PM
Not that it makes it right or wrong but I have mounted a gazillion disco's to RTU's.
Mounted directly to the unit on large units and various strut set-ups on others. The only issues I have had are: Do not mount to access covers. Do not mount over name plates. Do not screw into internal coils [Linked Image].
Posted By: Ryan_J Re: Rooftop unit follow-up - 04/08/04 04:07 PM
440.14
Posted By: DougW Re: Rooftop unit follow-up - 04/08/04 11:15 PM
When I worked at a local grocery store chain, I remember seeing several disco's mounted towards the corner of the units - the idea being, if the case becomes "hot", one can D/C the power by using a hot stick / "broom" stick, or other nonconductive means.

The D/C is also visible from 2 sides, and I've seen the units labeled with yellow and black "caution" style labels as to where the D/C's were, as well as information as to which panel they were being fed from.

Not a code requirement, of course, but a good idea nontheless.
Posted By: triple Re: Rooftop unit follow-up - 04/08/04 11:25 PM
Kentvw said it best. Follow those directions and you can't go wrong.

If you wire/ground correctly, how can the "case" become hot? If it is not wired correctly then no procedure for disconnect placement is going to make the set-up safe.
Posted By: maintenanceguy Re: Rooftop unit follow-up - 04/08/04 11:35 PM
Triple beat me to it. If everything's grounded properly, the disconnect's housing would be hot if the RTU cabinet was no matter how far away it was mounted.

And if it's right on the unit, The HVAC guy (That's usually me) never has to wonder if he's turned off the right switch. And do us a favor, mount your switch right above the equipment's data plate. When they're exposed to the sun and rain they fade so bad we can't read them but everytime I see a data plate under the disco, the plate looks like the day it was made. [Linked Image]
Posted By: triple Re: Rooftop unit follow-up - 04/08/04 11:37 PM
I do, however, like to mount the disconnect separate from the unit to facilitate that units removal/replacement in the future. Most of the time this is not very practical without a good deal of additional labor. Thus the disco gets screwed to the side of the rooftop unit.
Posted By: Redsy Re: Rooftop unit follow-up - 04/08/04 11:48 PM
I was thinking in terms of replacing the condensing unit, and having the disconnect flopping around on the ground in the meantime.
Posted By: big guy Re: Rooftop unit follow-up - 04/08/04 11:52 PM
redsy cheak this outhttp://www.electrician.com/2002nec1_8/2002_nec_files/frame.htm
you can get alot of info for here