Posted By: rizer trouble shoot HID light ? - 03/27/04 10:47 AM
can any one tell me what steps you would go through to trouble shoot an HID light ?
Posted By: electure Re: trouble shoot HID light ? - 03/27/04 12:46 PM
Rizer,
The steps involved, although basically the same, will depend on the type and size of HID light you're working on.
A very handy source of information is available from Advance Transformer.

CLICKHERE

It's also available in booklet form from them
...S

[This message has been edited by electure (edited 03-27-2004).]
Posted By: Scott35 Re: trouble shoot HID light ? - 03/29/04 02:43 PM
Rizer;

There are several methods for testing an HID fixture's components, some of which require basic testing items - others require advanced test equipment.
Also, the type of Lamp will greatly affect the testing principles.

Basic tests may be performed with simple DVMs, Ohm Meters and Ammeters.

Ohm Meters are used to verify continuity through the Ballast's Windings, through the Lamp Holder and to check the Capacitor (if used) for short / open conditions.

Volt Meters are used to check input Line Voltage, Open Circuit Voltage and Lamp Voltage (disconnect Pulse Ignitors when used).

Ammeters are used to check for Input "Idle" currents, and Short Circuit current levels.

Simple "Non-Tester" tests may be performed with Incandescent Lamps or Mercury Vapor Lamps placed in the circuit.

Testing things like the output of a Pulse Ignitor requires something that can withstand the high voltage pulses, and display their frequency + amplitude and duratin.
An Oscilliscope works best.

Testing an HID Lamp requires a Regulated Power Supply type of a test device.
A normal Ohm Meter will read infinite Resistance (like an open circuit) on a good Lamp.
They are Arc Tubes, so testing them requires advanced methods (or simply try using the Lamp in a known operable fixture of equal type - this is a very efficient and low cost test method!).

Let me know what type of tests you plan to perform, and I can give you some testing examples, which do not require the use of hi $$$ testers.

Need to know Lamp type (LPS / Merc / Metal Halide probe start, or HPS / MH Pulse start), and how large (Wattage) of Lamps.
Can give test examples to cover nearly all scenarios, but do not require expensive testers.

The link that Scott (Electure) provided is really good - and may have all you need.
If not, or you have additional conserns / questions, let me/us know.

Scott35
Posted By: rizer Re: trouble shoot HID light ? - 03/29/04 11:59 PM
thank you both i'm printing the adv.lighting troubleshooting section now and appreciate your answers!
© ECN Electrical Forums