Posted By: donles splicing grounding electrode conductor - 10/27/03 06:57 PM
Does any one splice or tap to the GEC?
What do you use? I'm upgrading a duplex with 100 amp panels side by side in the basement.
Rather than run two #6 solid cu from each panel to the ground rods outside, I'd like to run from one panel to the rods. Then run #6 from the 2'nd panel and tap onto the 1'st panel's GEC using irreversible compression-type connectors. I believe this is permitted by NEC 250.64 (C) and (D).

I've checked with 2 supply houses and they evidently do not carry a compression tool or the connectors. Anyone have experience with this?
Donles,
Burndy, Thomas & Betts, and Anderson are the ones that make the tools and materials off the top of my head. All of these can be found by a simple web search.

If you quit that solid habit, you can use a Cadweld, made by erico www.erico.com
These are reusable for a long time, and do not degrade like crimps or split bolts.
Posted By: donles Re: splicing grounding electrode conductor - 10/27/03 09:27 PM
What is the ballpark cost for Cadweld?

I've found the cost of the T&B tools to be prohibitive for my infrequent use. Although I did see a Penn-Union tool on ebay for what is probably alot less than retail. Minimum bid $99 for a TDM-250 and the auction was winding down.
I normally use a split bolt for this.
Posted By: Ryan_J Re: splicing grounding electrode conductor - 10/27/03 10:26 PM
Split bolts are not irreversible. Perhaps you're thinking of an equipment grounding conductor and not a grounding electrode conductor?
Posted By: iwire Re: splicing grounding electrode conductor - 10/27/03 10:37 PM
If you do a search on this site for cad welds you will find a thread that talks about one shot disposable cad welds for $5.00 I have not used them but it sounds like a great deal.
Posted By: donles Re: splicing grounding electrode conductor - 10/27/03 11:40 PM
I looked at Erico's site for the one-shot, inexpensive cadweld splices. Their site isn't the most user friendly. I did come across mold # PG11L for #4 solid to #4 solid taps but no details. I'll have to call suppliers tomorrow.
Thanks.
Posted By: eprice Re: splicing grounding electrode conductor - 10/28/03 12:10 AM
Ryan,

Couldn't 250.64(D) be used here, and wouldn't that allow the use of something like a split bolt to make a tap to a second enclosure as long as the GEC to the first enclosure meets 250.64(C) and is not spliced where the tap joins?
Posted By: Ryan_J Re: splicing grounding electrode conductor - 10/28/03 12:24 AM
EPRICE: Thanks! I got so caught up the topic starter's question of how to do it irreversibly that I didn't look at the code. Good catch.

Scott: Sorry!
Posted By: donles Re: splicing grounding electrode conductor - 10/28/03 01:20 AM
Care to expand on that a little?
Meanwhile, I'll consult the code.
Split bolts do the trick. I use them as described for multi family services.

[This message has been edited by Electricmanscott (edited 10-27-2003).]
I believe that the inexpensive exothermic welds being discussed are the One-Shot by Erico or the Uni-Shots by Harger. I use these quite often, anytime I must connect to a ground rod outside. But if memory serves me correctly, both these inexpensive tipes are used for rod to conductor connections. I think that for conductor to conductor or other configurations, you must use the standard graphite mold and charge version. I couls be wrong, but that's all I could find.
Posted By: donles Re: splicing grounding electrode conductor - 10/28/03 01:57 AM
I think I see what you mean. I initially thought that the tap connection had to be irreversible. That rule, 250.64(C) applies to a splice in the GEC.

250.64(D) allows taps to be made to the GEC by conductors from a second enclosure without saying how, just that the GEC must be installed without a splice or joint.

I was so focused on (C) that I neglected to carefully read (D).

Thanks
Posted By: PCBelarge Re: splicing grounding electrode conductor - 10/28/03 09:07 PM
Donles
You can use 250.64(D) for the two panels, but the common GEC has to be spliced with an irreversible type of connection.
Look back at (C).

Pierre