Posted By: ALWIRE Meter Cans and the Power Co. - 09/04/03 05:06 PM
When you must move/replace the meter can, do most EC's work it hot or call the power co. to shut off the power?
Just trying to get an idea of how this is usually handled.
Posted By: ThinkGood Re: Meter Cans and the Power Co. - 09/04/03 06:45 PM
First, I'm not an electrician. Second, I'm in New Jersey. That said...

From the few electricians I've spoken with around here, "by the time the POCO comes out..." I've seen them wire the meters while hot.

I have yet to see PPE used, except for when I did see someone from the POCO "cutting" my neighbor's new service after it was already installed. He had gloves and glasses. I'm not sure if more than that is called for on a residential meter.

I'm sure the others on the board here will have more information for you. Meanwhile, does anybody recall where the photo is of the meter that arc flashed?
Posted By: sparky Re: Meter Cans and the Power Co. - 09/04/03 07:08 PM
I usually cut an OH service, then do my work , why work it hot if you don't need to...?

This is contrary to poco rules, so i've researched the state laws here to make sure i'm ok, which i am
Posted By: Bjarney Re: Meter Cans and the Power Co. - 09/04/03 07:33 PM
Acceptable meter-socket models and their various distribution modes seem to be an intensely regional practice. The only aspect that offsets this variable a bit is that most large and a growing number of smaller utilities {of which there are no slight number in the US} are publishing their policies/specs at their websites.

{Read on only if you’re really, really bored…} There is one industry-standardization group Out West, but even within “EUSERC” the variety of drawings and specs for sockets above a residential 200-amp form-2S can be vast.

It is worth noting that typically a 'cold turkey' call to a utility meter department will guarantee strict “by trained stuntmen only“ orders that seals, meters and service-drop/-lateral conductors are not to be touched by non-utility personnel, but if you’re one of their established/local “good ol' boy” contractors, the practice is condoned and sometimes expected by them.

OTOH, way back when I remember one utility feigning convulsions while threatening to call the National Guard, Mental Hospital and Governor’s Office for doing the same. [They were also indeed most uncooperative and non-committal about responding to a disconnect and reconnect for a bonehead farmhouse service change. They were, however, good for sometimes leaving behind a very cool “Salisbury Joint Paste Pot,” canvas bucket or an occasional wood-handled Burndy MD-6 press, but if you wanted to get a service knob or a PG connector from them, you had to drive to their corporation yard on the opposite end of the county with a minimum 2-pound can of coffee as barter.]




[This message has been edited by Bjarney (edited 09-04-2003).]
Posted By: ALWIRE Re: Meter Cans and the Power Co. - 09/04/03 08:06 PM
Also, does the POCO generally charge to upgrade their wires to handle service upgrades in your jurisdiction? Here is CO, they're telling us $800-$1000 to upgrade their wires?
Posted By: Electric Eagle Re: Meter Cans and the Power Co. - 09/05/03 12:26 AM
There are occasions that we cut the tag and pull the meter, such as an emergency panel replacement.

Our Poco's don't charge for service upgrades, but they rarely upgrade their wire. If we upgrade someone to underground from overhead they will charge.
Posted By: sparky Re: Meter Cans and the Power Co. - 09/05/03 01:00 AM
ALWIRE, i suggest you do a little research into what i assume is poco competition, most states have legislative issues on line

example, Vermont Statues Annotated.......

Title 13, Chap 081, #3784 of the VSA....

Quote
3784. Interfering with meters
A person, other than an authorized agent or employee acting for the owner, manufacturer or operator thereof, who maliciously opens, closes, breaks into or in any manner adjusts or interferes with a meter, or other regulating or measuring device or appliance attached to or connected with wires, pipe lines, mains, service pipes or house pipes owned or used by a manufacturer or furnisher of electricity, gas, or water shall be imprisoned not more than three months or fined not more than $100.00, or both.
Posted By: HotLine1 Re: Meter Cans and the Power Co. - 09/05/03 01:33 AM
Overhead resi and comm up to 400 amp, 3 phase, we cut at the drop, do what is necessary, and then re-connect.

All of the above is done after a permit is obtained, and the utility is notified.

Meter can seals we cut, after advising the utility.

Upon approval of inspection by the town, a cut-in card is issued to the utility, and they re-seal and install their crimps on the drop.

Wait for the POCO; don't hold your breath around here. (Bless the deregulation)

John
Posted By: Ryan_J Re: Meter Cans and the Power Co. - 09/05/03 01:57 AM
Heres the part that drives me nuts. As already mentioned, the POCO rarely upsizes their service entrance conductors. That being said lets take this scenario: Existing 100A service gets changed to a 200A. New meter is installed, new panel, new breakers, yadda yadda yadda. What is unfortunate is that 250.66 (GEC sizing) is driven by the size of service entrance conductors. If the POCO doesn't change their wires, the electrician doesn't have to change the grounding electrode conductors. This would bother me if I paid for a service change...
Posted By: targetshootr Re: Meter Cans and the Power Co. - 09/05/03 10:24 PM
in nc, our local poco is immune from a lot of the code also. made me nuts when i first found out.

did a generator panel recently where they originally ran TWO underground runs of 350mcm/al into the ct cabinet on a 5000 sq ft house with gas heat. of course on an upgrade, they dont upgrade much if anything.

to the original question, i never have and never will kill anything on the line side of a meter. but i pull meters all the time and have no qualms about it.
Posted By: Rob528 Re: Meter Cans and the Power Co. - 09/08/03 09:01 AM
Hi, Does Detroit Edison still make the homeowner or the Electricain hook-up the service drop? Detroit edison stopped doing service hook-up's in the late 80's.


Thanks, Rob.
Posted By: iwire Re: Meter Cans and the Power Co. - 09/08/03 09:43 AM
Ryan,

Quote
What is unfortunate is that 250.66 (GEC sizing) is driven by the size of service entrance conductors. If the POCO doesn't change their wires, the electrician doesn't have to change the grounding electrode conductors.

You lost me here, even if this is an underground service the electrician replaced the wire from the meter to the panel right?

These are still service entrance conductors and the ground wire size are based on these.

Quote
Service Conductors. The conductors from the service point to the service disconnecting means.

If we sized the grounding conductor to the POCO wire that would be a big change as many times the POCO wires are 4 AWG or 6 AWG, at least for overhead.

Bob
Posted By: HotLine1 Re: Meter Cans and the Power Co. - 09/08/03 07:38 PM
Iwire: Ithought it was only me that had the same thoughts???

Ya beat me to the post again.

John
Posted By: Ryan_J Re: Meter Cans and the Power Co. - 09/08/03 11:33 PM
One of the things I love about these forums is that they keep you on your toes! Thanks for pointing that out to me Bob! I was thinking "service conductors" and not "service entrance conductors"...my bad [Linked Image] The type of change out I usually see is for an underground service and an "all in one" type of panel on the exterior. The only service entrance conductor "wires" you see are the POCO's, as the panel has bussing from the meter to the panel. When that occurs, do you consider the bussing to be the service entrance conductors and assume the equivalant rating of the panel for the size of them? Thanks again for correcting me Bob.
Posted By: iwire Re: Meter Cans and the Power Co. - 09/09/03 07:57 AM
Ryan, I was thinking about this while at work and realized that what I think of as a typical service is not how everyone does it.

I have never seen an all in one setup in this area, and an outside disconnect for a dwelling unit is very rare.

Here is note 3 from 250.66

Quote
3. Where there are no service-entrance conductors, the grounding electrode conductor size shall be determined by the equivalent size of the largest service-entrance conductor required for the load to be served.

It sounds like even if they install a 200 amp panel that they could size the GEC by the calculated load.

In the absence of load calculations maybe just have them size it to a 200 amp conductor?

Glad to help out, sorry if I came across to strong.

Take Care, Bob