Posted By: ga.sparky56 amperage - 08/01/03 03:52 AM
If I feed a 100a main lug panel with say a 40a dp breaker, do I have 40a total capacity? Or do I have 40a available on each leg for 120v loads?
Posted By: amp-man Re: amperage - 08/01/03 04:40 AM
Russell,

Look at it this way--

40A @ 240V = 9600 VA

and

9600 VA/120V = 80A

So, you've got 40A on each of the legs.

Cliff
Posted By: elecbob Re: amperage - 08/01/03 04:45 AM
If you touch each of the two little screw heads on the circuit breaker where the wires go with the test leads of a voltmeter and it says 208 or 240, you have 80 amps of 120 volt power available. That's assuming you have a neutral too. Of course.
(signed) Sorry. I forgot my name.
Posted By: ga.sparky56 Re: amperage - 08/01/03 10:36 AM
Thank you Cliff and Bob.