Posted By: NorthernLights Stove and Dryer Wiring Change - 04/08/03 02:10 AM
Why did the code change from a 2 w/ground to a 3 w/ ground on stove and dryers? Is it the increased electronic 110 loads involved in the new units? I have people ask me why the change was made in the code........honestly I never knew.

Thanks
Posted By: caselec Re: Stove and Dryer Wiring Change - 04/08/03 02:48 AM
The change your referring to I believe was part of the 96 NEC but don't have a copy in front of me right not to verify if this is the proper addition.

A neutral (grounded conductor) has always been installed as part of range and dryer circuits but it was also permitted to be used for grounding the frame of the range or dryer. New installations are now required to have an equipment ground wire run with the circuit. 250-140 (2002 NEC)

Curt
Posted By: Electricmanscott Re: Stove and Dryer Wiring Change - 04/08/03 10:54 AM
Good question. Anyone know the answer? I have never given it much thought, and I don't know the reasoning behind this change.
Posted By: Redsy Re: Stove and Dryer Wiring Change - 04/08/03 11:24 AM
I have heard that the practice was permitted in order to save on materials during the WW2 era. I guess that could be checked historically. The practice was allowed to remain because of it's "good track record" regarding safety. Overall though, it is not an ideal method (problems can arise during renovations when service panels become subpanels) and the time finally came to prohibit it.
Posted By: ThinkGood Re: Stove and Dryer Wiring Change - 04/08/03 01:59 PM
Here are some threads from this board that might help with an answer:
https://www.electrical-contractor.net/ubb/Forum5/HTML/000270.html
https://www.electrical-contractor.net/ubb/Forum1/HTML/002305.html
https://www.electrical-contractor.net/ubb/Forum1/HTML/002267.html
Posted By: C-H Re: Stove and Dryer Wiring Change - 04/08/03 06:19 PM
Perhaps simply a question of consistency: If circuits with common neutral and equipment ground (TN-C) isn't allowed in other cases, why should it be allowed for stoves and dryers?
Posted By: SvenNYC Re: Stove and Dryer Wiring Change - 04/09/03 03:15 PM
A three-wire electric stove or dryer plug and cord would be like this:


Hot #1, Neutral, Hot #2

240 volts across hot #1 and hot #2. 120 volts across each hot and the neutral. You would also have to bond the chassis (the metal case) to the neutral.

A four wire plug and cord would be like this:



Hot #1, NEUTRAL , Hot #2

EQUIPMENT GROUND

The added ground (always a green wire in the cord) is to bond the metal housing of the device to EARTH, so that way if any loose current-carrying conductor were to short-circuit with the metal cabinet the charge would get safely carried to the ground instead of through YOU.

The voltages across the two hots and across each hot and neutral (the white wire in the cord) are the same as the three wire configuration. There must be no voltage across neutral and ground (EARTH) conductors!!

I tried to use the simplest layman language I could to explain this. Please correct me if I have made ANY error. [Linked Image]

[This message has been edited by SvenNYC (edited 04-09-2003).]
Posted By: Electricmanscott Re: Stove and Dryer Wiring Change - 04/09/03 03:56 PM
I am thinking nobody knows the answer to this one. Myself included.

[This message has been edited by Electricmanscott (edited 04-09-2003).]
Posted By: CTwireman Re: Stove and Dryer Wiring Change - 04/09/03 05:05 PM
I have heard the WW2 explanantion too, although I don't know why the practice continued long after the war was over. I would guess there are millions of 3 wire feeds going to dryers and stoves.
Posted By: Bjarney Re: Stove and Dryer Wiring Change - 04/09/03 06:37 PM
So why the neutral in the first place? AIUI, electric ranges used 120V for lower heat, and 240V for higher. 120V clocks and a convenience outlet on electric ranges were once common. For dryers, the motor has been classically 120V and the heater 240V. I don't know of that's the case for new appliances.
Posted By: txsparky Re: Stove and Dryer Wiring Change - 04/09/03 06:44 PM
I posed this similar question awhile back as to why Type SE was allowed to be used but not Type NM. To me a bare wire being used for neutral is a bare wire being used for neutral. One of the replies that I recieved from Joe T. was that the CMP just decided to draw the line somewhere,with no given explanation [Linked Image] . It's a d**m shame they couldn't explain their reasoning a little better.

[This message has been edited by txsparky (edited 04-09-2003).]
Posted By: classicsat Re: Stove and Dryer Wiring Change - 04/09/03 07:31 PM
FWIW, in Canada, the code, as far as I can remeber, has been to install 3w+G to range/dryer installations. I have only seen the outlet type associated with 3 prong ranges used for old 220V/50A welders.