Posted By: CTwireman THW wire - 03/30/03 05:28 PM
I have 2 old spools of THW wire. Is is permissible to use this anymore?

I am thinking about using it feed a tool shed through 3/4 pvc.

If not, I will be taking a run to the scrap yard.

Thanks,
Peter
Posted By: iwire Re: THW wire - 03/30/03 05:35 PM
It is listed in 310.13 as OK for dry and wet locations, there is no reason not to use it.

Remember if you run out more than 1 circuit you will need a ground rod out there.
Posted By: CTwireman Re: THW wire - 03/30/03 05:41 PM
Thanks Bob. It's for a single circuit, so I don't have to worry about the ground rod.
Posted By: Ron Re: THW wire - 03/30/03 09:41 PM
THW is a great conductor as its insulation is more durable (thicker) during a pull through conduit. It is rated for wet environment, as underground installation must be considered.

[This message has been edited by Ron (edited 03-30-2003).]
Posted By: NJwirenut Re: THW wire - 03/30/03 09:43 PM
Doesn't "THW" signify THermoplastic, Wet location?
Posted By: Bjarney Re: THW wire - 03/31/03 12:13 AM
The H in THW probably designates it as 75°C insulation, versus TW being 60°C. In a number of areas, it was the default industrial building wire before THWN/THHN was popular. Earlier, THW aced out RHW with improved ease of handling.

[No hepcat electrician would use solid TW if he could get stranded THW.] At one time, TW was available in solid up to 6AWG.




[This message has been edited by Bjarney (edited 03-30-2003).]
Posted By: kale Re: THW wire - 03/31/03 05:25 PM
"THW----PVC insulated building wire. Flame-retardant, moisture and heat-resistant, 75deg C. Dry and wet locations."

From Essex Wire&Cable Reference Guide 1997.

[This message has been edited by kale (edited 03-31-2003).]