I have 2 old spools of THW wire. Is is permissible to use this anymore?
I am thinking about using it feed a tool shed through 3/4 pvc.
If not, I will be taking a run to the scrap yard.
Thanks,
Peter
It is listed in 310.13 as OK for dry and wet locations, there is no reason not to use it.
Remember if you run out more than 1 circuit you will need a ground rod out there.
Thanks Bob. It's for a single circuit, so I don't have to worry about the ground rod.
THW is a great conductor as its insulation is more durable (thicker) during a pull through conduit. It is rated for wet environment, as underground installation must be considered.
[This message has been edited by Ron (edited 03-30-2003).]
Doesn't "THW" signify THermoplastic, Wet location?
The H in THW probably designates it as 75°C insulation, versus TW being 60°C. In a number of areas, it was the default industrial building wire before THWN/THHN was popular. Earlier, THW aced out RHW with improved ease of handling.
[No hepcat electrician would use solid TW if he could get stranded THW.] At one time, TW was available in solid up to 6AWG.
[This message has been edited by Bjarney (edited 03-30-2003).]
"THW----PVC insulated building wire. Flame-retardant, moisture and heat-resistant, 75deg C. Dry and wet locations."
From Essex Wire&Cable Reference Guide 1997.