Greenies or splice caps? (assuming appropriate wire count)
Posted By: sparky66wv Re: Yet another... - 06/21/01 01:19 PM
Splice caps... they take up less room.

And something about making EGC splices with irreversible pressure connectors...
Posted By: resqcapt19 Re: Yet another... - 06/21/01 02:49 PM
Sparky66wv,
Are you telling us that splice caps are required????????????
Don(resqcapt19)
Posted By: Redsy Re: Yet another... - 06/21/01 03:51 PM
Quote
Originally posted by sparky66wv:
Splice caps... they take up less room.

And something about making EGC splices with irreversible pressure connectors...
Are you confusing EGC (250-148) with GEC(250-64 (c))with regard to irreversible ?

[This message has been edited by Redsy (edited 06-21-2001).]
Posted By: sparky Re: Yet another... - 06/21/01 10:49 PM
splice caps? you mean the barrel crimps?
Posted By: sparky66wv Re: Yet another... - 06/22/01 12:15 AM
You're right Redsy, I'm mistaken...
however...


250-148 states:

"...The arrangement of grounding connections shall be such that the disconnection or removal of a receptacle, fixture, or other device fed from the box will not interfere with or interrupt the grounding continuity."

Any reasonably experienced "handyman" knows that it is easier to remove a receptacle (if it is pigtailed) by removing the wirenuts than it is to wrestle the wrapped wire off of the terminal. In replacing a receptacle, said handyman may choose to remove the greenie in lieu of unscrewing the ground screw. With barrel crimps, this proves to be rather difficult.

Perhaps this is very arguable, I'm not really saying it is code, but I feel that barrel crimps do offer many advantages in EGC situations.