Posted By: Yoopersup Tracking Live wires . - 04/29/16 09:12 PM
What do they make that you can trace a wire from Device or Motor to the Panel to get the correct circuit without shutting the power off. Some of the loads run 24/7 And are not marked correctly.
Both 3 phase & single phase.
Thank you
Yoopersup
Posted By: gfretwell Re: Tracking Live wires . - 04/30/16 07:29 AM
There are breaker finders that insert some kind of signal on the wire that you can pick up with the tester at the breaker end. The one I have is 120v only tho (a wall wart looking sender). I put a 1-15 receptacle on a pigtail with some insulated clips so I can use it on a circuit without a receptacle handy.
Posted By: twh Re: Tracking Live wires . - 04/30/16 04:22 PM
I tried a couple different tracers that are plugged into an outlet and have had some success and some failures. When I'm turning off a plug circuit that really has to be right, I built a box with a 4 amp cycling load so I can verify the circuit with a clamp-on ammeter.

A telephone toner will work on a dead circuit.
Posted By: brsele Re: Tracking Live wires . - 04/30/16 11:36 PM
Originally Posted by twh
I tried a couple different tracers that are plugged into an outlet and have had some success and some failures. When I'm turning off a plug circuit that really has to be right, I built a box with a 4 amp cycling load so I can verify the circuit with a clamp-on ammeter.


So can I ask what do you use for cycling?
I've been looking for one of those flashers people used to use at Christmas, but they don't sell them where I am.

Thanks
Posted By: twh Re: Tracking Live wires . - 05/01/16 06:00 AM
For a cycling load, I have a couple magnetic heaters inside a 10x10 JB with a heat sink from an old VFD opposite the heaters. They cycle on for about a second and off for about 3 seconds.

It takes about one second for an ammeter to give a good reading. The off time is longer to reduce the heat.

I have an ammeter with forks that slip over the wires so I don't have to clamp on to each wire.

Sometimes the panel feeders have a steady enough load that the phase can be determined, which reduces the number of tests on breakers.

This is a result of an incorrectly labelled breaker that the circuit tracer also incorrectly identified. It's a funny thing. If the power goes out on computers, everyone goes outside for a smoke. If an electrician makes a mistake, they want to see blood on the walls.
Posted By: gfretwell Re: Tracking Live wires . - 05/01/16 05:43 PM
Quote
It's a funny thing. If the power goes out on computers, everyone goes outside for a smoke.


Trust me, when the computers are down, there are still plenty of people who want to see some blood on the wall. wink
Posted By: Yoopersup Re: Tracking Live wires . - 05/02/16 03:39 AM
Most the Loads I am talking about are 3 phase 480 v motor loads.
120 Volt loads are not a problem/
Still Looking