Posted By: jdevlin multiwire circuit - 01/13/03 11:51 PM
Here is question that was posed today. Can anyone tell if it would violate any code.
A mutli wire circuit with both branches off the same leg using #14 wire and the neutral using #10. Since #10 is rated for 30 amp would there be a code violation.
NOTE:No one is actually trying this is was just a question that was raised.
Posted By: HotLine1 Re: multiwire circuit - 01/13/03 11:54 PM
A handle tie on the OCP???
I'm OK with the #10 neutral, and you do have 15 amp OCP on the two hots right??
John
Posted By: jdevlin Re: multiwire circuit - 01/13/03 11:56 PM
Yes 15 amp ocp. The handle tie never came up in the discusion.
Posted By: iwire Re: multiwire circuit - 01/14/03 01:19 AM
Do you mean to say both hots on the same phase?

That will make for a strange handle tie.:
Posted By: HotLine1 Re: multiwire circuit - 01/14/03 02:05 AM
Iwire:
OK, you're awake. I should have said something like " a tandem/piggyback breaker" with a handle tie.
John
Posted By: lighthouse Re: multiwire circuit - 01/14/03 02:47 AM
jdevlin...this is one practice that i never liked.i under stand that your running less wire(cost)but if you lose the neutral you could have 240 volts going to a receptacle.

i know they do sell this cable.standard mc cable with a super neutral.but i think it/'s 3#12 and a#10 neutral and a #12 ground for a 3 phase panel .don't no if it comes in #14/w 10 neutral.

i don't see a violation here.15 amp ocp and a #10 neutral.better then the 14/3 used and someone changes the breakers around.
Posted By: Hutch Re: multiwire circuit - 01/14/03 03:34 AM
If you're on the same leg I don't see the 240V problem with the lost neutral.

In that regard, a tied pair of breakers should be required for code but I've never seen these tied across the same leg. Can you tie your own?
Posted By: iwire Re: multiwire circuit - 01/14/03 03:36 AM
I am still confused

jdevlin said

"A mutli wire circuit with both branches off the same leg"

Article 100: Branch Circuit, Multiwire
makes clear that the hots are from different phases

If this is the case all #14s would be fine

But "with both branches off the same leg"
this would not be a multiwire branch circuit, it would be two hots of the same phase coming back on one neutral
the current would add up to potentially 30amps
never seen this done (On purpose) and my reaction would be that it is a violation,
But I do not know how to find it.

lighthouse we do this all the time with 4 wire 3H + 1N + 1G the advantages outway the problems for us.

And for the cables AFC will pretty much get whatever you need.

I just did a job using MC with 3 whites 2 greens 1 each black red blue all #10s Matched up to the office cube furniture
Posted By: lighthouse Re: multiwire circuit - 01/14/03 04:04 AM
Hutch..your right there no way you can get 240 volts on the same circuit.i was just trying to explain this circuit on two seperate circuits breakers.myself i just don't like this practice.

iwire..office cube furniture.3 circuits w/1 isolated ground.receptacles mark a,b,c. nice you can change the receptacles to whatever circuit you like.
Posted By: jdevlin Re: multiwire circuit - 01/14/03 12:11 PM
Please not I am not attempting to do this. It was just a discussion that came up as to wether it was a code violation or not IF it was done.
Posted By: Redsy Re: multiwire circuit - 01/14/03 12:27 PM
The question may have originated with 225.7 which permits a similar principal for outdoor lighting equipment. However, as you describe it above, this is not a multiwire ckt. I, personally, would never do this. If for no other reason than it is not in accordance with conventional wiring practices. And that is a good enough reason for me.



[This message has been edited by Redsy (edited 01-14-2003).]
Posted By: electure Re: multiwire circuit - 01/14/03 12:54 PM
This Q has been run in both this BB and the MHE forum in the past.
The way it was originally asked by jdevlin,
it's perfectly legal. (without handle ties).
If it were in fact a multiwire circuit, with say 4 #14 hots (2 per Ø), and a #10 grounded conductor, it's perfectly legal. (the handle ties would only be required in a dwelling where the multiwire circuit supplies devices on one yoke, or one piece of equipment. Commercial, no handle ties if the loads are all line to grounded conductor.

The loss of the grounded conductor on a multiwire circuit, although it can lead to elevated voltages, will not put 240 volts to any single device unless the impedance on the opposing leg is 0 ohms.(dead line-noodle short). It is a series circuit once the grounded conductor connection is removed, with the loads on both legs in series.
Posted By: electric-ed Re: multiwire circuit - 01/14/03 01:37 PM
This sketch might help explain what electure is saying.

The over-voltage resulting from an open neutral on a multi-wire circuit will depend on how well the load is balanced.

The sketch shows what I would consider an extreme case, and it definitely would cause damage.

In circuit A the voltages across the two loads are approximately equal because of the intact neutral conductor.(The line voltage drops are not calculated here).

With the neutral open (circuit B) the 10 ohm and 30 ohm loads are in series for a total of 40 ohms. There is a damaging overvoltage on the 30 ohm load, due to the unbalanced load. If the load were perfectly balanced, there would be no voltage difference.

[Linked Image from electric-ed.com]

Ed


[This message has been edited by electric-ed (edited 01-14-2003).]
Posted By: resqcapt19 Re: multiwire circuit - 01/14/03 01:57 PM
I've always been taught that you can't use a common neutral for multiple circuits unless it is a multiwire circuit, however I can't find a code rule that says this. I have found rules that, in specific cases, permit a common neutral, but not rules to prohibit one. The rules that permit common neutrals are, 215.4(A)and 225.7(B).
Don
Posted By: Joe Carpenter Re: multiwire circuit - 01/14/03 02:05 PM
It seems to me the question is not about a multiwire circuit. Are you asking about running 2 #14 "hots" off one leg (1 single pole breaker) and only 1 #10 grounded conductor? If so, yes it would work although like you said, I cant think of any reason why to do it.
Posted By: lighthouse Re: multiwire circuit - 01/14/03 04:25 PM
electure...ok maybe 240 volts was a little high.but i had a service call last year and if i remember right i had 190 to 200 volts on the receptacle.more than enough to burn out there appliances,etc.after checking the circuit i found and overheated neutral on the neutral bar.(loose connection.)like i said i don't like this practice.but that's just me.
Posted By: jdevlin Re: multiwire circuit - 01/14/03 06:09 PM
You are correct it is not really a multi wire circuit. That was the best I could come with for a short topic. It is LIKE a multiwire with 2 breakers only both are on the same phase. This would mean that it is possible to have 30 amps on the neutral. Since #10 is rated 30 amps then would it be ok to use as a common neutral. No one could come with a code section that it would violate.
It was regarding a regular residential service. No 3 phase. Once again I would not attempt this is was just a discusion that came up.
I never thought this would cause so much discusion.

Thanks for all the comments.
Posted By: electure Re: multiwire circuit - 01/15/03 01:06 PM
Thank you, Ed.
I'm sure that made my raving and ranting much easier to understand!

I didn't mean to get carried away with the bolds, no offense meant to anyone.
I've seen the same "lost neutral" comment made 3 or 4 times in as many weeks on another electrician BB, and it's a shame...S
Posted By: John Steinke Re: multiwire circuit - 01/17/03 07:56 PM
I believe that "multiwire circuits" are an exception to the rule of 1 hot = 1 neutral. I also am under the impression that the only place that different neutrals are allowed to come together is at the panels' neutral bus.
Even if I am wrong about the language of the code, I would still avoid this situation because if I turned off one of the feeds, and disconnected the neutral, I would have a "hot" neutral were any load on the other circuit be 'on.' That, in turn, would make it kind of hard to truly 'lock out' anyhting on the circuit being worked on.
So how do you do this legally? Install a sub-panel.
Also note that some panels -zinsco comes to mind- have "double" breakers draw from different legs of the panel.
Posted By: electure Re: multiwire circuit - 01/17/03 09:06 PM
John,
Belief #1 is correct. The impression, #2 is not.
Multiwire circuits are used extensively.
Scenario Subpanel. The subpanel in itself is a fed by a Multiwire circuit (the feeder).