Posted By: Cinner 480 v hps lighting circuit - 03/02/12 09:12 PM
I was working on a 480v hps lighting circuit and went to turn the circuit off to change the fixture but still measured 66 volts to ground on each leg. Does. Any one know why this would be?
Posted By: LarryC Re: 480 v hps lighting circuit - 03/02/12 10:15 PM
What type of meter did you measure the voltage with? If it is an electronic meter with the high input impeadence, it will measure "ghost" voltages. These "ghost" voltages are due to the wires traveling next to energized wires. Both set of wires are acting as a transformer.

Measure the voltage with a Wiggy or equivalent and the voltage will PROBABLY disappear. If they do not disappear, you have a problem. If the voltage does disappear then you are measuring ghost voltages.
Posted By: Cinner Re: 480 v hps lighting circuit - 03/02/12 10:22 PM
Measured it with a fluke multimeter.
Posted By: Tesla Re: 480 v hps lighting circuit - 03/03/12 01:37 AM
Fluke multimeters ARE high impedance testers.

You need to use an old-style analog meter to load down these induced voltages. Since there is no current flow, it's really a capacitive effect.

Posted By: HotLine1 Re: 480 v hps lighting circuit - 03/03/12 03:21 AM
Cinner:

You need a 'Wiggy', or any other brand solenoid type tester, or an analog multi-meter.
Posted By: sparkyinak Re: 480 v hps lighting circuit - 03/03/12 08:26 AM
WIGGGGGGGY!!! I carry one in my pouch just for that
Posted By: Lostazhell Re: 480 v hps lighting circuit - 03/03/12 10:36 PM
This happens in a cogen I work in alot.. 480V wiring from VFD loads seem to induce voltage on other conductors more than anything.. HID loaded circuits have the same tendency