Posted By: bwise121 Difference in AC and DC disconnects - 04/25/11 07:36 PM
I just put in my first DC disconnect and for the life of me I can't see what the physical difference is. Besides the fuses is there a difference? Is there such a thing as a non-fused disconnect?

Thanks,
Byron
Posted By: Vindiceptor Re: Difference in AC and DC disconnects - 04/25/11 07:56 PM
Is this a PV DC disconnect?

Some manufacturer's have different arc chutes and most will require the use of multiple poles being used to facilitate the breaking of the DC arc.

Square D and Siemens both have wiring diagrams, have not used a Cutler-Hammer Disconnect yet.

Yes, you can get them as non-fused.
Posted By: bwise121 Re: Difference in AC and DC disconnects - 04/25/11 08:47 PM
Yes, it is a 30 amp disconnect for a PV system.
Posted By: gfretwell Re: Difference in AC and DC disconnects - 04/25/11 08:58 PM
You can usually put a big diode across a DC contact to put out the fire.
Posted By: Vindiceptor Re: Difference in AC and DC disconnects - 04/26/11 12:50 AM
Originally Posted by bwise121
Yes, it is a 30 amp disconnect for a PV system.


2 or 3 pole and how did you route the circuit through the disconnect?

What's the Isc for the circuit? That would determine whether you can run the circuit through a single pole, 2 or three (when 2 is required and you have a fuse, some manufacturer's want the fuse in the center pole 'B phase').

You can NOT route a circuit through a single pole and maintain the UL listing of the switch, Square D used to imply that you could, but they have since reworded their documentation.

I'm only mentioning this because I've seen a LOT of botched/non-code compliant designs and installs using 30, 60, 100 and even 200 amp 600 VDC disconnects with 3 circuits going through them.

We have been using combiner boxes with integral DC disconnects since mid 2009 because of the confusion with AHJ's, unfortunately, most don't even know what they're looking at when they're inspecting them, but they are definitely getting better and more informed since the PV market blew wide open.
Posted By: LarryC Re: Difference in AC and DC disconnects - 04/26/11 05:38 PM
You can usually put a big diode across a DC contact to put out the fire.

How will that help if the load is not inductive? The diode shorts out the inductive kick from a collapsing magnetic field because the induced voltage is the opposite polarity. A diode or even a RC network across contacts won't do much if the DC load is not inductive.
Posted By: gfretwell Re: Difference in AC and DC disconnects - 04/26/11 05:57 PM
Non inductive loads break cleaner.
Posted By: Tesla Re: Difference in AC and DC disconnects - 04/26/11 09:37 PM
The DC from PV arrays is NOT an infinite bus.

It breaks MUCH cleaner for that reason.

There is only so much energy flowing into the PV cells.

So even shorted PV DC does not produce the astounding arcs expected.

Not that I'd recommend trying it.