Posted By: SJT Gas Stations - 10/27/10 03:04 AM
Hello,
We were checking a job in a stock room of a gas station. They want to install wall switches to turn the pumps on and off. (Morning and night) The owner presently operates the Ckt. Breakers in the panel. Am I allowed to install a wall switch between the breaker and the wiring going out to the pump? The breaker looks like a 2 pole, but there are breakers that also breaks the nuetrals for pumps? I have not seen the inside of the panel yet. If it is that type of breaker, can I install a normal Single pole switch, or must I break the nuetrals also, like the breaker is doing? I just thought that possibly, the breaker is rated SWD, then he could keep it as is.
Thanks
Posted By: harold endean Re: Gas Stations - 10/27/10 01:49 PM
SJT,

First thing I would do is to check the breaker to see if the breaker is SWD rated then nothing has to be done.
Posted By: HotLine1 Re: Gas Stations - 10/28/10 01:53 AM
Harold:

Looking into SWD 240.83(D) of '08 I only see text regarding switching of fluorescent lighting, and an HID marking for switching HID lighting.

Interesting?

Thinking further into the OP, I wonder if there is a EPO (emergency off) for the dispensers, or might these be old fashioned pumps?

Sorry, but I have more questions than an answer!