Posted By: Edward Buck and boost transformers - 12/14/02 09:07 PM
I am planning to install a buck and boost transformer to buck 277 to 240 to operate two motors one @ 15 Amps and other @ 24 Amps single phase.
The NEC 99 does not state anything about the secondary protection do i need a load center/subpanel on the secondary side of the transformer to protect the two loads?
The NEC 99 450-4 does not say anything about that except not put a OCPD in series with the shunt winding.

Edward
Posted By: Bjarney Re: Buck and boost transformers - 12/15/02 02:45 AM
Try http://www.federalpacific.com/literature/drytrans/FPTS-RTB-0701.pdf -- page 11+