Posted By: rcksmith127 208 volt contactor - 02/24/09 01:13 AM
Need some help. Are there voltage ranges for a coil? I have a 3 phase 208 volt 3 hp motor with a NEMA Size 1 contactor with a 208 volt coil and a start/stop built in.
After the initial smoking of the coil, it had a 24volt coil instead of the 208 volt varity the box label stated. Lesson learned...
Anyway, I now have the correct coil but it won't pull in, it chatters. I read the voltage to actually be about 225 volts between phases which is not something I have come across much in this neighborhood.
Is there a "range" that the coil should work in? This started as a simple "favor" for a friend and it is turning into more of a time consuming problem.
Any input is appreciated.

Posted By: ghost307 Re: 208 volt contactor - 02/24/09 02:42 AM
Chattering is often the result of installing a DC coil on an AC control circuit.
When the drops to zero (before reversing polarity) the coil loses its field and the contactor starts to spring back open.
Posted By: gfretwell Re: 208 volt contactor - 02/24/09 02:44 AM
Is this the type with a pick and hold coil, selected by a side switch? You may be wired to the hold side.
Posted By: smokey Re: 208 volt contactor - 02/24/09 04:08 AM
i am experiencing the same problem with a set of contactors that control heating elements for a water heater.they keep chattering .even after replacement.i am now in the process of replacing them with a larger contactor 70a instead of 50a .i am thinking that the load is to much for the contactor.im not sure if this is helpful to you.im not sure if the higher voltage would effect the contacts inside the contactor.
Posted By: JBD Re: 208 volt contactor - 02/24/09 05:01 AM
Load does not affect the contactor sealing in.

The three most common reasons that contactors make noise are:
Low coil voltage. Most coils will pull in at 85% and drop out at 65%.
Jammed mechanism from dust or worn slides.
And probably the most common; rust, dirt, or scratches on the magnet poles faces which prevent them from mating correctly.
Posted By: SteveFehr Re: 208 volt contactor - 02/24/09 02:02 PM
It could simply be defective from the factory. We ran into a few defective chattering contactor solenoids last year in an application where problems like that are unheard of (high-end UPS systems).

It can be hard to tell the difference between a wrong part and a defective one, especially if you're pulling the replacements from the same defective batch.
Posted By: JBD Re: 208 volt contactor - 02/25/09 12:33 AM
One more question.

You say it does not pull in, it just chatters.
Do you mean that it chatters while you hold the Start button in and then it drops out when you release the button?
Not holding in would be caused by a bad holding circuit contact or a wiring error.
Chattering, like rapid pickup then dropout, could be a wiring error where a contact from the starter is actually turning the circuit off instead of holding the circuit on.
Posted By: mb95307 Re: 208 volt contactor - 02/25/09 02:24 AM
Most contactors are equiped with a shaded pole. This shaded pole holds the contactor shut while the AC current crosses the zero point. If it is chattering, this is the first thing that I would look for...
Posted By: gfretwell Re: 208 volt contactor - 02/25/09 02:26 AM
got my attention...
Posted By: SteveFehr Re: 208 volt contactor - 02/25/09 01:39 PM
Originally Posted by mb95307
Most contactors are equiped with a shaded pole. This shaded pole holds the contactor shut while the AC current crosses the zero point. If it is chattering, this is the first thing that I would look for...
How does that work, are there two solenoids in the contactor, one with a straight winding and one with a shaded pole?
Posted By: rcksmith127 Re: 208 volt contactor - 02/25/09 04:37 PM
The night I installed this it was late. I wanted to go home, the customer wanted to go home so I didn't get ample time to look at everything. The original plug that was on the starter, yes it was pluged in, had a 250 volt plug on it. Perfect, mount the new starter, install the start stop and all should be well.
What I found the next morning was that the motor was wired for 480v. It would run but it ran wierd.
Now that it is re-wired for the 208 volt being supplied it is running fine.
It's been a while since I took something for granted (original wiring being 208 volt based on attached cord and plug). Another reason it is important to check everything and not take it for granted.
Posted By: mb95307 Re: 208 volt contactor - 02/25/09 05:38 PM
The shading coil is a rather large copper band around the laminations of the metal core of the contactor. When a magnetic field is present on the core from the main coil, it induces another current in the shading coil through basic transformer action. This current is about 90 degrees out of phase with the primary current and peaks when the when the current in the primary coil is crossing the zero point, therefore maintaing a magnetic field on the contactor keeping it closed duiring this time.

It the shading coil were to burn out, which happens quite often because of the large amount of current present on the coil, it cannot hold the contactor closed during the zero crossover causing a chatter to become obvious on the contactor.

From Wikipedia: If the coil is designed to be energized with AC, a small copper ring can be crimped to the end of the solenoid. This "shading ring" creates a small out-of-phase current, which increases the minimum pull on the armature during the AC cycle.[1]
Posted By: ghost307 Re: 208 volt contactor - 02/25/09 06:53 PM
One trick that I was taught if the shading coil was broken or fell off was to take some scrap wire and loop in where the shading coil was. Make a good connection at the ends and it should hold together long enough until the new coil that you ordered arrives.
Posted By: gfretwell Re: 208 volt contactor - 02/25/09 06:57 PM
Interesting.
I have seen big contactors with 2 coils. One is a low resistance coil that pulls in the armature and then the side switch flips to a higher resistance coil that holds it. You will see wires running around the outside of the coil to the switch. Get that wired wrong and it won't pick.
Posted By: JBD Re: 208 volt contactor - 02/26/09 01:05 AM
A shading coil is a copper loop that is inserted into the steel 'core' of the electromagnet assembly. The copper loop causes the flux in the steel core (that it surrounds) to change slowly. The result of this, is a portion of the steel core remains magnetized during the zero cross over point of the AC voltage.

A broken shading coil can cause a 60 cycle hum (not including a shading coil is one way to make an electric buzzer).
Posted By: JValdes Re: 208 volt contactor - 02/27/09 08:33 PM
There are contactors available that are energized electrically, then held mechanically. They have a name but I cannot remember what they are called. I will check further for you.
This solved chattering problems in the past.
Posted By: renosteinke Re: 208 volt contactor - 02/28/09 01:30 AM
"latching relays"
Posted By: electure Re: 208 volt contactor - 03/01/09 09:48 PM


Or "Mechanically Held Contactors" smile

Posted By: JValdes Re: 208 volt contactor - 03/04/09 06:21 PM
Yes, mechanically held contactors. I got this from micromind today. I hope this helps.

"These devices are known as mechanically held contactors. I've seen them made by square D, GE, and others. They come in multi-pole (2 through 12 poles), and panelboard types. The panelboard type mounts inside of a panel, just like a main breaker. It turns the whole panel on and off.

The multipole type that I installed last was a Square D class 8903 type LX. It was 30 amp, 6 pole, and controlled 6-277 volt parking lot light circuits.

They work like this; if the contacts are open, the close coil is energized. As soon as the contacts close, there is a 'clearing contact' built into the unit that de-energizes the closing coil. The contacts are held closed by mechanical means. Even if all power is lost, the contacts will stay closed. The control voltage can be pulsed or continuous.

When the contacts need to be opened, control voltage is sent to the open coil. There is a similar clearing contact here as well. The contacts are now held open by mechanical means.

The main advantage here is no coil noise. Either coil is energized only momentarily, so no buzz or hum. The disadvantage is that if you're using a photocell or time clock, you'll need a small 'ice cube' relay to control the contactor coils. NO is connected to the close coil, NC to the open".

Courtesy Rob (micromind)
Posted By: gfretwell Re: 208 volt contactor - 03/05/09 02:03 AM
IBM called them a latch/trip relay (used in logic circuits). When relays were replaced by silicon they became flip latches. (AKA flip flops)
Posted By: JoeTestingEngr Re: 208 volt contactor - 03/06/09 03:45 AM
Most of the mechanically held lighting contactors that I've seen are more like a solenoid that drives a linkage over center on a cam. The contactor is either forced closed by the cam or allowed to spring open. The cam also switches a form c contact set with the "a" contact going to the "Open" terminal and the "b" contact going to the "Close" terminal. The common goes to the hi side of the coil. The contacts just have to stay closed long enough to guarantee that there is enough inertia to get the linkage over center. Even a mechanically held contactor will chatter or buzz if it doesn't make it.
Joe