Posted By: Ellis Commercial switch gear - 01/23/09 07:38 PM
I had someone put a screw into an 800 amp branch circuit cable when replacing the panel cover. does anyone know of a publication or standard that states to inspect behind the screw holes before replacing panel? this person did no work on the system, simply removed the front panel did a visual for available breaker positions and replaced the panel. He recieved only lightly singed eyebrows and a stain in his shorts.
Posted By: HotLine1 Re: Commercial switch gear - 01/23/09 08:57 PM
First guess would be 'common sense'..but that's not in the NEC

Second is workmanlike manner.

Stained shorts and singed eyebrows? Buy a lottery ticket, he's one lucky guy!

Seriously, I can't think of any standard other then 110.3 (b); mfg instructions as a longshot.

Posted By: maintenanceguy Re: Commercial switch gear - 01/24/09 12:21 AM
This is not an answer to your question but a related story.

We opened up a 200A 208/120 panel about a year ago to add a couple of circuits. Started wiggling wires in the panel and found one wire that we couldn't move. Investigated and found out that a company that had installed some steel shelving in the storage room behind the panel had screwed their shelving into the "metal wall panel" in the closet. Of course the metal wall panel was the back side of the electrical panel.

They had put a self tapper right into the neutral feeder. Talk about luck.
Posted By: EV607797 Re: Commercial switch gear - 01/25/09 02:47 AM
Sorry for the continued sidetrack. Common sense really is rule #1, but you won't find that written anywhere. I never replace the cover on anything without double-checking clearances of screws. I don't care if I just took the cover off two minutes earlier.

What amazes me is when the factory screws get lost and someone replaces one or more with 2" sheet metal screws. Talk about blind luck!
Posted By: Ann Brush Re: Commercial switch gear - 01/26/09 10:11 PM
Why are the screws for the cover of residence panel 1" long when they only need to be 1/2 or even 1/4". I mean its only 2 layers of 1/16 sheet metal?
Posted By: NORCAL Re: Commercial switch gear - 01/27/09 12:08 AM
If a cover on a piece of equipment is removed the one reinstalling it has the responsibility to make sure screws do not penetrate any insulation and if dealing w/ a older panelboard where they use concealed clamps to hold the panel front to also make sure they don't pinch anything. You take it off, you are responsible to see that everything is clear to replace it.......
Posted By: HotLine1 Re: Commercial switch gear - 01/27/09 01:02 AM
Norcal touched on where I intended to go. 'Workmanlike' manner is directed to the person who is re-installing the cover; it must have been 'good' before it was removed.

I have come upon a few conductors that were 'close' on inspection, ad noted them accordingly.
Posted By: Scott35 Re: Commercial switch gear - 01/27/09 08:48 AM
As stated by others, there is no documented text in the NEC, but there is some "hinting" done in a few of the Switchgear installation manuals I have read over the Years.

On one of the bulleted lines, there is a paragraph describing to "Check For Pinched Wires When Replacing Covers".

And, as stated by others, it's something to commonly think of when replacing covers, and such.

When dealing with large Feeders in switchgear sections, the Conductors tend to naturally want to spring right against the brackets where the screws for covers are affixed to.
This is apparent prior to installing the covers, and steps should be made to secure the Conductors away from the landing brackets (to avoid a Ground fault issue from a Bolt/Screw penetrating a Conductor's insulation).

With Panelboards, Branch Circuit Conductors should be routed away from possible conflicting areas, such as where the Mounting Holes are located, or where captive clamps will engage the Enclosure.

Screws / Bolts of proper length should be used, and these should have "Dull" or rounded ends.

There are times when a Panelboard was made up in an "Ugly" fashion!
These Panels resemble a tightly packed Bird's Nest inside. Typically, the Covers on these Panels will "Spring Off" when the screws are loosened!
Re-installing the Covers on these Panels is a challenge, to avoid pinching Conductors, or driving a screw through Conductors.

Scott
Posted By: gfretwell Re: Commercial switch gear - 01/27/09 07:30 PM
They could fix this problem if the cover mounted on studs with wing nuts or knurled caps instead of screws that penetrate the wiring cabinet.
It would be easier to put on too since it would hang there until you got the nuts started.
Posted By: renosteinke Re: Commercial switch gear - 01/28/09 12:00 AM
Sure would, Greg!

Ironically, someone once posetd a pic here of a panel with this exact 'field modification,' and wanted to kiow what part of the NEC was violated! frown
Posted By: gfretwell Re: Commercial switch gear - 01/28/09 03:09 AM
I suppose the only complaint might be that since you didn't need "tools" to get in it you were encouraging unqualified people to look around.

The more I think about it the more I want to do it on my panels. I was careful to be sure I only used the regular 10-32 type screws (not the double speed ones) so I could just swap them out with 3/4" hex heads run from from the inside and knurled nuts.
Posted By: Pierre Re: Commercial switch gear - 01/28/09 07:15 PM
There is no standard other than NFPA 70E for the incident that occured as related in the thread.

70E and the requirements set forth in the document would have most likely precluded the individual from ever removing the screws from the panel cover.

if he is an employee, then OSHA, which references 70E, would apply to the individual we are discussing.
Posted By: HotLine1 Re: Commercial switch gear - 01/28/09 10:51 PM
Pierre:

A BIG 'welcome back'!

Posted By: waymag Re: Commercial switch gear - 02/04/09 03:23 AM
I have a nomex suit that I use ANY time I get into an electrical panel. It is my company's policy. Anything can happen inside. Remember the handyman may have been in there.