I'm sitting here reading the tech data sheet for a Siemens type P1 panelboard. I noticed that one of the available breakers listed (Type BGL) has a note #2. Looking at the bottom of the page, note #2 reads:

"Two pole breaker is one phase and neutral, Three pole breaker is two phases and neutral."

What does that mean? I don't have this panel or plan to order it, I just wonder what such a panel would be used for.
Posted By: EV607797 Re: Neutral through breaker? - 12/05/08 06:55 PM
I has been a long time, but I seem to recall something similar being required for gasoline pumps. I haven't worked with that stuff in years, so don't quote me on that.
Posted By: HotLine1 Re: Neutral through breaker? - 12/05/08 11:06 PM
That may be the panel that the AFCI's go into that do NOT come with neutral pigtail, only a load neut/line termination.

Time permitting, I have to read more on this
Posted By: wire_twister Re: Neutral through breaker? - 12/06/08 12:22 AM
Possibly for shunt trip breakers??
Posted By: NORCAL Re: Neutral through breaker? - 12/06/08 04:13 PM
It's where a neutral is req. to be switched, and the accessory requires one additional pole space just like a shunt trip.
Posted By: walrus Re: Neutral through breaker? - 12/06/08 11:11 PM
Its a switched neutral 2 or 3 pole breaker, used to break all conductors. Its just a switch on the neutral side as far as I know. Use them all the time in gasoline installs
Posted By: kohli Re: Neutral through breaker? - 12/06/08 11:35 PM
This breaker is to be used for gasoline pumps or other places where you need to brake the netural also when you turn off the circut
Posted By: pdh Re: Neutral through breaker? - 12/08/08 02:03 AM
They should just run the pumps on 2-wire 240V and not worry about switching a neutral since there won't be one (at least in North America).