About a year ago IAEI magazine was touting some new galvanized ground rod (basically a planted story and a paid ad). This month they have an article trashing them. Their tests predict you may only get 10 years out of one.
Their credibility is wearing pretty thin with me.
We really need to separate the manufacturers from the code making and code enforcing community.
Posted By: renosteinke Re: Galvanized ground rods - 09/17/08 04:51 PM
I have not read the article to which you refer, but I'd like to point out:

You have never been required to use a special rod as a ground rod. The NEC details pipe, rod, and other made electrodes. There's no reason even a simple piece of #5 rebar can't be used as your electrode.

What the NEC has specified is that rods smaller than the code specified size need to be listed as such. That is, smaller than the 5/8 the code calls for. That's why the galv rod makers passed out those little 'gages.'

Corrosion of ground electrodes has been looked at recently, and there have been plenty of unhappy surprises. It seems that, in very many ordinary situations, the performance and life of the rods and plates is a lot less than was expected. In some reports, the absolute worst results were from ... big surprise here ... rods made of stainless steel. Oops.

Posted By: dougwells Re: Galvanized ground rods - 09/17/08 04:59 PM
If we use a ground rod in Canada it has to be listed.
Posted By: brsele Re: Galvanized ground rods - 09/18/08 12:12 AM
Originally Posted by dougwells
If we use a ground rod in Canada it has to be listed.


Really?
I've never noticed any special markings on any rods or plates I've installed.
Do you have a code reference?

Thanks... Bruce
Posted By: dougwells Re: Galvanized ground rods - 09/18/08 12:24 AM

10-700 Grounding electrodes (see Appendix B)

(1) Grounding electrodes shall consist of

(a) manufactured grounding electrodes;
(b) field-assembled grounding electrodes installed in accordance with this Rule; or
(c) in-situ grounding electrodes forming part of existing infrastructure as defined in this Rule.

(2) Manufactured grounding electrodes shall

(a) in the case of a rod grounding electrode, consist of 2 rod electrodes (except for a chemically charged rod electrode where only one need be installed) spaced no less than 3 m apart,

(i) bonded together with a grounding conductor sized in accordance with Table 17; and
(ii) driven to the full length of the rod; or

(b) in the case of a plate electrode, be

(i) in direct contact with exterior soil at no less than 600 mm below grade level; or
(ii) encased within the bottom 50 mm of a concrete foundation footing in direct contact with the earth at not less than 600 mm below finished grade



appendix B

D
Rules 10-700(1)(a), 10-700(4)

Manufactured grounding electrodes are those manufactured and certified to CSA C22.2 No. 41.
It is important that in-situ grounding electrodes provide an equivalent surface area contact with earth as do manufactured electrodes (see CSA C22.2 No. 41). Consideration should also be given to the effects that corrosion may have on the in-situ ground electrode impacting durability and life-expectancy. For example, an underground metal water piping system located at least 600 mm below finished grade and extending at least 3 m has traditionally been recognized as a suitable grounding electrode. Similarly, the metallic reinforcement of a concrete slab, concrete piling, or concrete foundation and iron pilings in significant contact with earth at 600 mm or more below finished grade have also been found to be suitable in-situ electrodes.
Any metallic material encapsulated with a non-conductive compound to protect it from corrosion would not meet the criteria for use as in-situ ground electrode.



Posted By: brsele Re: Galvanized ground rods - 09/18/08 12:51 AM
Thank you for the info.
I guess that's one of the differences between the CEC and the OESC.

Cheers... Bruce
Posted By: gfretwell Re: Galvanized ground rods - 09/18/08 02:21 AM
The Local IAEI has had a lot of conversations about rods too. The consensus is all of them rot out pretty quick down here. I was really surprised that anyone would even consider galvanized.
I know right after I moved in here I was fixing a piece of 12ga Romex going out to the dryer in the garage and I buried THWN/EMT. About 2-3 years later I had cause to dig it up. The EMT was just a rusty trail in the sand with little chunks of rusty metal in it.
Right now our defacto ground electrode is a ufer.
Posted By: Elviscat Re: Galvanized ground rods - 09/18/08 05:30 AM
Originally Posted by renosteinke

Corrosion of ground electrodes has been looked at recently, and there have been plenty of unhappy surprises. It seems that, in very many ordinary situations, the performance and life of the rods and plates is a lot less than was expected. In some reports, the absolute worst results were from ... big surprise here ... rods made of stainless steel. Oops.



How does this work? do the alloying metals in the SS make it more prone to galvanic action than regular or galvinised steel?

How soon until we need catodic protection systems with sacrificial anodes to go with our ground rods?

Personally, I've always been of the opinion that ground rods don't provide an adaquate path to ground regardless of state of decomposition.
Posted By: Trumpy Re: Galvanized ground rods - 09/18/08 07:54 AM
Originally Posted by Elviscat

How does this work? do the alloying metals in the SS make it more prone to galvanic action than regular or galvinised steel?

How soon until we need catodic protection systems with sacrificial anodes to go with our ground rods?

Personally, I've always been of the opinion that ground rods don't provide an adaquate path to ground regardless of state of decomposition.


Bear in mind Will, that there are over 90 types(grades) of Stainless available.
One thing that has to also be remembered about stainless, is the fact that it contains a fair amount of Nickel and Chromium, Nichrome wire is used for heating elements.

Down here in damp New Zealand, earth electrodes can have a very short life, especially near the coast.
As an inspector, the Earthing test is often the first to be done when checking out faults.
Our supply system depends on good earthing, to clear faults on the system, with reasonably large fault currents being sent down the Earth circuit, back to the transformer.

I have, before today buried heavy copper wire in the soil as an alternative to an actual stake in the ground, where the soil is too stony to get an effective earth.

Some people over here (even some electricians) have the tainted idea that an earth electrode should last the life of the building.
Umm, no, it might if your soil has a neutral pH, but these are few and far between.

In a totally safe building, there should be no current flow in the earth electrode at all, this is not achievable, there will always be a small amount of current flow there, this is what causes galvanic corrosion, to a degree.

The other part is the fact that the metal-soil contact area, is often not a 100% thing due to stones and other larger particles in the soil.
Posted By: renosteinke Re: Galvanized ground rods - 09/18/08 03:03 PM
All I can do is report the results .... I can't claim to 'know' why.

One theory that has been advanced is that, as with aluminum, the presence of oxygen is necessary for the formation of a rust-stopping oxide film, and that the lack of oxygen prevents this film from forming. Naturally, then, something else needs to be there to react with the metal, if not oxygen.
Posted By: SteveFehr Re: Galvanized ground rods - 09/18/08 04:33 PM
I think there are some misconceptions here. Galvanization does not inhibit corrosion, it only inhibits corrosion of the steel- the zinc coating starts corroding the moment it hits the ground. Though the zinc-oxide forms a coating that slows the reaction, a typical zinc galvanized coating will be gone in 7-15 years, and the bare steel below will rust to nothing extremely quickly. Thicker zinc coatings would last longer, as might new zinc-aluminum alloys, which also hold some promise.

The stainless steel rods discussed above are not solid CRES, but merely have a CRES sheating around a standard steel core. And hold up up rather well.

The standard copper-clad ground rods still see some corrosion of the steel core, but also hold up very well.

Driving a bare uncoated piece of steel in the ground is a very bad idea.

Good report here:
http://www.transorbelectrical.com/pq/technical/Electrode_Life_Rempe.pdf

Quote
Galvanized steel rod: “Most of the galvanizing had been lost. Rusting of the steel was greatest near the surface of the ground. Pitting was worst here and near the tip.

”Stainless-clad steel rod: “The cladding was free of corrosion, but at the tip the steel core had corroded to a point about 1 inch inside the cladding.

”Copper-clad steel rod: “The copper cladding was virtually free of corrosion, but the steel core had corroded at the tip to a point 2 inches inside the cladding.”

The study concluded, “Magnesium, aluminum, zinc, mild steel, and galvanized steel rods did not have the desired corrosion resistance.” There was a concern about the copper clad rod causing galvanic corrosion to coupled mild steel. The amount of galvanic corrosion caused by coupling copper and steel will vary depending on their ratio. Since the ratio of steel to copper in most grounding systems is usually large, the amount of steel corrosion is negligible. Additionally, there are often other sources of copper in the ground, which can add to galvanic corrosion concerns. Two studies have now been examined that clearly show the corrosion difference, and therefore expected life, between galvanized and copperbonded rods.
Posted By: renosteinke Re: Galvanized ground rods - 09/19/08 03:32 AM
Steve ... be careful of your knowledge.

The study I based my comments upon used solid stainless, in both rod and plate form, in Southern Nevada and Southern California. In this study, even after only five years, very little was left of the electrodes.

As I mentioned, there's a lot that is not yet known. I suspect we'll find that there is no such thing as a 'good everywhere, all the time' material.

I also suspect that a lot of what we "know" about ground rods, etc., is based more upon 'logic' than actual experimentation ..... not to mention outdated theories and assumptions.
Posted By: SteveFehr Re: Galvanized ground rods - 09/19/08 01:20 PM
There are a lot of different "stainless" steels, too. Technically, they're referred to as CRES, corrosion resistant steel, and underground is a very harsh environment for any ferrous alloy.

One thing they have in common, though, is that they're all going to corrode slower than ordinary carbon steel. I would not be surprised to see some grades of CRES rust out before a copper clad rod, but I'd expect every single one to outlast a piece of rebar.

Can you post some more information about the studies you're referring to?
Posted By: renosteinke Re: Galvanized ground rods - 09/19/08 01:43 PM
Alas, I cannot ... at this time. The %$&^ study is still on-going, and no official report has been issued as yet - though that has not stopped the participants from going on the seminar circuit.

I am also quite interested in the specifics; the assertion that even plain, low quality steel out-performed the stainless has me more than a bit curious.