Posted By: mj double lug, how to aviod it?> - 11/16/02 06:24 PM
what wrong with making other connections at an termnial block, then cary one conductor to the ocpd ? any other ideas ?
Posted By: spyder Re: double lug, how to aviod it?> - 11/16/02 06:26 PM
Can you give an example of the situation you are refering to?
Posted By: HotLine1 Re: double lug, how to aviod it?> - 11/18/02 12:35 AM
Are you talking about putting multiple conductors in a mechanical lug???
Good worknmanlike practice, and the NEC prohibit that, unless the lug (termination) is listed/rated for multiple conductors. Said listing/rating is ususlly indicated on the flat of the lug/termination.
John
Posted By: Scott35 Re: double lug, how to aviod it?> - 11/19/02 03:22 AM
Not a bad idea - kind of what's going on with Grounded Conductors and EGCs.

Panel would require ample free space to do this, plus most likely need UL / Manufacturer's listing and "A-OK"

It would be a much cleaner looking alternative to using a Wirenut, but would be a higher cost item - per materials and labor.

Scott s.e.t.