Posted By: JuddsAirco Rotary Phase Converter - 11/11/02 04:52 AM
I have a fire department that needs a 3 phase 5hp pole mount rotary siren to be installed. They do not have access to 3 phase power. Need to know if a rotary or static phase converter is more practical and which is easier to install. Done plenty of 3 phase wiring but never had to fool with converters before.

[This message has been edited by JuddsAirco (edited 11-11-2002).]
Posted By: Bjarney Re: Rotary Phase Converter - 11/11/02 05:37 AM
There’s probably no rule of thumb, but you may want to limit total voltage drop {on 1ø and 3ø sides} to 3% running {and 15% during starts.} Current on the 1ø side will likely be ~twice the 3ø current—1.73x+converter loss.

http://www.gwm4-3phase.com
http://www.phaseconverter.com
http://www.ronkelectrical.com

Voltage imbalance [ø-ø, not ø-grd] can be a significant contributor to stator-heating problems in the process.



[This message has been edited by Bjarney (edited 11-11-2002).]