Posted By: steve ancient apprentice Residential question - 09/28/07 12:02 AM
As most of you know i do very little resi work but today i came accross in a attic j-box 5 neutrals and 5 neutrals spliced together with a single # 12 neutral as a jumper between the two. although properley rated for the 20 amp ccircut is this permissible? I am very concerned as this is the bosses license going on this job. I will talk to him tomorrow and the inspecction on our work is monday but you thoughts and comments are apprecciated . This is a 1950s prefab house which we did the service changeover & a new garage. I opened the box cause i found 3 romex cables going into one connector.A violation in itself. Eagle eyes with Bi-focals. Thanks gang. Always Steve
Posted By: Tiger Re: Residential question - 09/28/07 03:25 AM
Usually connections are made like this to fit the wire nuts. I don't know of any violation. Personally, I'd put them all together with a split bolt.

Dave
Posted By: SteveFehr Re: Residential question - 09/28/07 10:27 AM
If it's all fed from the same 20A circuit and connections made per UL listings, it shouldn't be a problem. Now, box fill and wire nut rating might come into play, too... how many #12 is a red nut listed for? Are they all securely in the nuts?
Posted By: gfretwell Re: Residential question - 09/28/07 03:23 PM
Sounds more like a place for a blue one.
Posted By: JValdes Re: Residential question - 09/28/07 04:21 PM
Do they still make those "crimp sleeves" with the rubber boot. Now that is a good connection. But I do not think they are suited for solid wires.
Posted By: steve ancient apprentice Re: Residential question - 09/28/07 10:46 PM
I talked to the boss today and took a picture of it to show him with the digital camera. He said not a problem we just put a box extender on the J-box and i made sure all the connections were secure and took one of the romex cables out of the clamp and put it in a new knockout with a cable clamp. Thank you all for your input really appreciate the info. We even go a little more business out of this home owner cause i told them if they run a couple of air conditioners on the same circut they will continually trip the breaker. We run a couple of new circuts this weekend. BOSS IS HAPPY.
Aways,
Steve
Posted By: macmikeman Re: Residential question - 09/28/07 11:36 PM
Otherwise known as a bridge splice. Not a problem if done as described in the original post.( as the others have stated)