Posted By: etech Single phase 480v lighting circuit - 08/11/07 02:24 PM
Need to install 3 480v single phase parking lot circuits on contactor. Can I get by with a 3 pole or do I need to go with a 6 pole? Must I break both conductors?
Posted By: iwire Re: Single phase 480v lighting circuit - 08/11/07 02:39 PM
Originally Posted by etech
Need to install 3 480v single phase parking lot circuits on contactor. Can I get by with a 3 pole or do I need to go with a 6 pole? Must I break both conductors?


In my opinion 410.54(B) requires you to switch all ungrounded legs supplying the 'auxiliary equipment' (AKA the ballasts).
Posted By: etech Re: Single phase 480v lighting circuit - 08/11/07 02:43 PM
Thanks!