Posted By: bwise121 How to phase a motor - 05/01/07 10:17 PM
I've been asked to phase a 3-phase motor. I'm not sure if this is normally the electrician's job or the HVAC's. What type of meter do I need and what is the process?

Thanks,
Byron
Posted By: RobbieD Re: How to phase a motor - 05/02/07 12:25 AM
Question-

Do you just have to do a rotation test?

or

Do you have this 3 phase motor and all of the winding connections are all apart and you need to connect them up?
Posted By: bwise121 Re: How to phase a motor - 05/02/07 12:39 AM
Rotation test only.
Posted By: RobbieD Re: How to phase a motor - 05/02/07 12:56 AM
If its for a piece of equipment that won't mind it going the wrong way for a short time then I would just do the 50/50 test. If you find it going the wrong direction just change it. No meters required just eyes.

Posted By: bwise121 Re: How to phase a motor - 05/02/07 01:16 AM
But... if I want to meter it and have it going the right way to begin with?

Posted By: togol Re: How to phase a motor - 05/02/07 01:34 AM
there are two types of phase rotation meters one requires line voltage to operate and the other is self-powered to check motors that are unwired...or going back into service

you use the powered type by connecting the three meter leads to your source voltage usually at the equipments last termination such as a starter or disconnect to verify your incoming voltage...and if you have an arrow on the motor..you then connect the motor leads 1,2,3, for the correct rotation..which as I recall is CCW opposite the shaft end

if you want to check a dead motor and can turn the shaft, use the self-powered type ...again connecting the meter leads to the motor leads and turn the shaft

several are available from Fluke, AEMC, Knopp,....
and Ideal makes a multimeter that you can use


Posted By: togol Re: How to phase a motor - 05/02/07 01:48 AM
BTW, in my opinion the Fluke is overpriced at almost $200.00

the AEMC PMR-2 is the most economical, <<<<I own this one

while the Knopp is the most rugged and has been around a long time
Posted By: togol Re: How to phase a motor - 05/02/07 02:47 AM
and there are several to choose from right here at the ECN Store