Installed a new 208 volt photo cell for some parking lot post lights. Tied 120v line to black, and load to red, and white to neutral, and the other 120 volt phase side goes to the other side of the lights. But it is not working. This comes from a 3 phase 120/208 volt panel. So it switches one side of the 2 - 120's. (opposite phases of course). Should be simple. The lights work when I bypass the photo cell. Am I forgetting something? Is there a different photo cell for panels with a wild leg? (208 to neutral).
Posted By: frenchelectrican Re: 208V Photo Cell.. doesn't work - 03/27/07 03:38 AM
Aldav53 :

are you sure this is a wye connection system or delta system ??

because the standard 120 volt photocell will not work with wild leg unless you got multivoltage photocell.

and how many lumiaiares you are controling this photocell ?
is there a contractor or mag switch ??

once i get this info we can work it out in correct way

Merci , Marc
Posted By: e57 Re: 208V Photo Cell.. doesn't work - 03/27/07 08:14 AM
Originally Posted by aldav53
Installed a new 208 volt photo cell for some parking lot post lights. Tied 120v line to black, and load to red, and white to neutral, and the other 120 volt phase side goes to the other side of the lights. But it is not working. This comes from a 3 phase 120/208 volt panel. So it switches one side of the 2 - 120's. (opposite phases of course). Should be simple. The lights work when I bypass the photo cell. Am I forgetting something? Is there a different photo cell for panels with a wild leg? (208 to neutral).

Sounds like you have let the smoke out of it.... And it sounds like you have a 240 delta panel? What voltage are these lights?

Normally I take a 120 photo cell and operate a 120 coil contactor from it. The photo cell also has a max amperage that you may have exceeded. But it sounds as though your photo cell got 240 though the load from the other leg.

Sorry 'bout all the colors - just messing with the new tool box up there...
Posted By: RODALCO Re: 208V Photo Cell.. doesn't work - 03/27/07 10:16 AM
Exactly what i wanted to say too e57.
Let the photocell control a contactor which can control the lights over 2 or 3 phases.

Also the current rating of these photocells is not that high, (10 Amps) An excessive load, which may cause the contacts to fuse together when overloaded. bear in mind the inrush currents of ballast lamps, SON is quite often a lot higher than the running current when warm.

Check with the info on the lightcell box, packaging, what the current rating is and which wire is incoming phase, load, and neutral.
Posted By: aldav53 Re: 208V Photo Cell.. doesn't work - 03/27/07 03:41 PM
No contactors or switches. Its for 208/240/277v photo cell. Not multi tap. Controlling 4 - 400 watt MH parking lot lights. Drawing 6 amps. All 3 phases 120v to ground, no wild leg. Just have the photo cell in line with one of the phases, Black in, red out, white to neutral.
Posted By: aldav53 Re: 208V Photo Cell.. doesn't work - 03/27/07 03:51 PM
Haven't checked the transformer, but what would be the difference if it was a delta or wye?
Posted By: aldav53 Re: 208V Photo Cell.. doesn't work - 03/27/07 05:38 PM
Do I hook the other side of the phase (120v) to the neutral on the photo cell? That would put 208v on the photo eye element.
Posted By: aldav53 Re: 208V Photo Cell.. doesn't work - 03/27/07 06:04 PM
This is a intermatic k4223c model photo cell.
208-277v 15a.
Posted By: Luketrician Re: 208V Photo Cell.. doesn't work - 03/27/07 07:34 PM
If it's 6 amps per light, e57 & RODALCO would be right. The photocell is only made to carry the control current. Not the actuall load current that you are trying to control.
Posted By: ShockMe77 Re: 208V Photo Cell.. doesn't work - 03/27/07 08:06 PM
(4) 400 watt lamps operating at 208 volts is less than 8 amps.

But (4) 400 watt lamps operating at 120 volts is over 13.

Is your source 120 or 208?
Posted By: RODALCO Re: 208V Photo Cell.. doesn't work - 03/27/07 10:12 PM
If the cell info says 208 - 277 Volts it needs that between phase and neutral.

Otherwise the bimetallic strip will not heat up enough, or the internal electronics doesn't work at the undervoltage of 120 Volts.

Normally at switch on (daytime) the load should come on for about a minute and then switch off, to show that the circuit works.

If the lights stay on, either the control voltage is not correct 120V instead of 208 - 277V or the contacts have fused together because of overload.
Posted By: e57 Re: 208V Photo Cell.. doesn't work - 03/27/07 10:38 PM
Originally Posted by aldav53
No contactors or switches. Its for 208/240/277v photo cell. Not multi tap. Controlling 4 - 400 watt MH parking lot lights. Drawing 6 amps. All 3 phases 120v to ground, no wild leg. Just have the photo cell in line with one of the phases, Black in, red out, white to neutral.


Whats the phase to phase voltage? (A-B, B-C, A-C) If all are roughly 240 - its a delta. But you say all 120 to ground... 208 phase to phase, with all 120's is a wye system. Just wondering why you mentioned a high-leg earlier???? As you would only get one on a delta....

As mentioned, the initial current can be much more, and can fuse contacts on you. And it may seem contradictory - but that unit may only be rated at 1700VA at that voltage?

http://www.intermatic.com/Default.asp?action=prod&pid=9163&sid=237&cid=52&did=5


I can find the wiring diagram on intermatics site for that model #, but it sounds odd that if it has a neutral it being rated for 208~277. And couldnt tell if that white were to be phase connected for 208 or 240???? Still got the destructions?????

It may have this in it:
Quote
Note that multi-voltage models self-adjust for the voltage. Models rated for 120-277 volts will not
work on 120-volts once used on 208-277 volts.


Heres another fun one - I've made this mistake before - Did you wait a while for it to come on? Sometimes it takes ~10 minutes...
Posted By: Rewired Re: 208V Photo Cell.. doesn't work - 03/27/07 10:46 PM
From what I read I think you are only feeding 120V to the eye element.
The neutral or rather the WHITE wire off the photo-eye will have to be connected to one of the phases.. If you have your lights wired between say B&C phases, then connect the photo eye between B&C or whatever you are using..
Better yet, picture it like a standard 120V circuit, where one of the phases is your hot, but the other phase you use is "neutral" even though it isn't and wire it up as if its a regular 120V circuit..

A.D
Posted By: Scott35 Re: 208V Photo Cell.. doesn't work - 03/28/07 12:44 AM
aldav53 ,

Connect the White Control Circuit Lead off the Photocell, to the other side of the 208 Volt 1Ø Circuit.
The Photocell's internal Relay Coil is designed to be driven from 208 Volts up to 277 Volts, so the Control Circuit must be within those parameters.

As it is now, the Control Circuit is only being driven at 120 Volts, so that internal Relay is most likely trying to pull in (may even be an audible "chirping" sound emitted).

I do agree with the use of Lighting Contactors for this type of Lighting option - mostly because the Photocell leaves a "Live" Ungrounded Conductor at each of the Fixtures when they are off during daylight hours, and someone may get "Shockenzeeassennoffer" (Shocked) if servicing a Lamp - due to the Screwshell being "Hot" still.

Multipole Contactors with all Ungrounded Conductors run through them, would reduce the potential for "Shokkenzeeassenoffer" by opening all the Ungrounded Conductors, plus eliminate the large load through the Photocell.
Not that this is a "Must Do" thing - you likely bid the job using a simple Photocell for the sole controller, and this is code compliant.

Anyhow, simply connect that White Lead to the "Other Side" of the 208 Volt Lighting Circuit, and the thing should work.
The Photocell's relay lead is "White" by "Default", so don't let that confuse you.
The White wire you used for the Photocell may be used to pull in a "Non-Identified Color" (i.e. Black, Red, Blue), which may be terminated to the "Other Side" of the 208 Volt Circuit at a convenient point - or if both Ungrounded Conductors run through the same box where the Photocell is at, simply terminate the White Photocell lead to the "Other Side" of the Circuit at that box.

Good luck! Let me know if smoke comes out wink
Posted By: aldav53 Re: 208V Photo Cell.. doesn't work - 03/28/07 01:40 AM
Found out, hooks in lineBlack in red out with the 120v side and the load side ties in with the white.
Posted By: e57 Re: 208V Photo Cell.. doesn't work - 03/28/07 03:10 AM
"load side ties in with the white"

Dont ya mean with the other phase the load is controlled with? As writen it would sound like the load were through the photo cells control side.
Posted By: NORCAL Re: 208V Photo Cell.. doesn't work - 03/28/07 04:02 AM
Correct me if I am wrong.... It seems to me your trying to run the photo cell with 120 volts, there is no neutral connection on a 208 0r 240 volt photo control, and a 400W MH is 2.3 A. @208V, a contactor controlled by PC, or PCs in each fixture might be another option.