ground wire and rods
-
11/25/00
05:16 PM
at a seperate building even if you run a ground with your wiring do you still have to install a ground rod at the seperate building
Posted By:
resqcapt19
Re: ground wire and rods
-
11/26/00
02:25 AM
A grounding electrode system is always required at the second building unless it only has one branch circuit feeding it. See 250-32(a)
Don(resqcapt19)
©