Posted By: EVAD7 AC DISCONNECT - 06/19/02 07:13 PM
FOR RESIDENTIAL AC COMPRESSOR HOOK-UP--2002 CODE WILL NOW REQUIRE A 120V OUTDOOR RECEPT. IS THERE A DISCONNECT OR A METHOD TO REDUCE INCREASED COST AND WORK FOR INSTALLATION?
Posted By: Ron Re: AC DISCONNECT - 06/20/02 12:17 AM
Place the compressor close to the recept provided in the front or back of the house.
Posted By: Electric Eagle Re: AC DISCONNECT - 06/20/02 01:56 AM
I'm sure some company will start making one, but I don't really see the need. The disconeect will surely cost a good bit more than a cheap A/C disconeect and the contractor will pay for the one you have to install and it won't be that expensive anyway.
Posted By: arseegee Re: AC DISCONNECT - 06/20/02 02:34 AM
Not to mention that you pull a 10/2, 8/2, or 6/2 to a 240v compressor which means you have no neutral to serve a 120v recept.