Posted By: Redsy Don't look at me... - 04/17/02 01:08 AM
Who, ultimately is responsible for an installation meeting code?

Scenario #1-
A large facility hires a contractor to install electrical equipment, but doesn't bother to oversee the project. The installation doesn't satisfy code requirements, but is accepted and paid for. Who is (ultimately) at fault?


Scenario #2-
A bid is submitted and accepted based on faulty drawings. During construction, the problem is discovered. It will add 10% to the overall cost. Who eats the 10?
Posted By: HotLine1 Re: Don't look at me... - 04/17/02 01:36 AM
Here in NJ the Lic. Contractor is responsible for the installation.

The second issue, depending on the "notes" on the prints, the contractor can be liable for "mistakes" on prints. Notes to the effect of "verify conditions in field" "site inspection required prior to submitting bid", or other legal jargon to this effect. Also, the size of the job has impact, and you may "Change Order". A good relationship with the Project Manager, or GC also helps. But, most of all PLAN REVIEW and read and understand the notes and specs

John
Posted By: HotLine1 Re: Don't look at me... - 04/17/02 01:39 AM
Redsy:
Also, here in NJ, the State UCC (Uniform Construction Code) states wording to the effect "DO NOT PAY CONTRACTOR FINAL PAYMENT UNTIL FINAL INSPECTION IS OBTAINED/APPROVED"

PS: I'm not "yelling".

John
Posted By: The Watt Doctor Re: Don't look at me... - 04/17/02 02:59 AM
Scenario #1
The large facility pays for the work, and not many days hence it blows up and kills somebody. If I installed it, I would have to live with the fact that I killed somebody because of my faulty work. The letter of the law doesn't really matter to me, but I would be willing to bet that some "hot shot" smooth talkin' lawyer would "prove" in a court of law that "I done it".

Scenario #2
I look at drawings everyday for the purpose of submitting proposals. If an error in the drawings is found before bid day, submit the problem through the "general" to the architect. The architect works with the consulting engineer, the correction is made, and an addendum to the bid documents is issued. When the proposal is made on bid day, always include the number of addenda that were received, and submit it writing on your propsal.
Now, say for example, not one person who looked at the drawings saw any mistakes, and at some point in the construction of the project the mistake is discovered that results in additional cost. They must pay for it. Nothing is free. There is much sculpatory language written into specs that does not amount to a "hill o' beans". If it costs more they must pay, and don't settle for anything less. Electrical Contractors are not design specialists. They are installation specialists, and if the engineer, or whoever, designed the project makes a mistake, the EC is not responsible. Think about it. When was the last time an engineer submited his plans to an EC for review. He calls up and says, "Mr. Electrician, I know that you have a license, and well, I'm a registered professional engineer, with an education in physics, math, etc, etc, etc, but I'm just not sure that I designed the service for that one man crapper correctly. Would you be so kind to sign your name on the drawings, and take responsibility for something that I'm being paid to take responsibility for?"
I have no intent of being offensive here, but I've grown weary of these GC's, architects, engineers, etc that think that they can screw up, and place the blame on the EC. I can tell you that if the shoe was on the other foot, and I left something out of my proposal, I wouldn't see a dime for it. [Linked Image]

I just vented.......
Doc

P.S.
What would keep "owners" from paying the engineers to put as many mistakes in the drawings as possible, and then holding the EC resposible for what he doesn't "catch"? It doesn't work that way. [Linked Image]

I just vented again....
Posted By: sparky Re: Don't look at me... - 04/17/02 09:27 AM
I'm with ya doc', all this 'trade malpractice' rolls downhill & gains speed as it goes....

In our litigate society, there seems a fixation not on who was in the wrong, but who has the $$$. After all, should Homer Simpson fall into the one man crapper ( while eating donuts) his lawyer will focus on the easy kill...

The other vouge thing is disclaimers.
"Caution this coffee will boil yer gonads off"
" Caution, contains phynetylenaprigummahummanol, do not chew gum & walk"
this, to the extent of CYA in every respect.

Perhaps the Q could be posed Here

...stated the nazi before the nueremburg tribunal " But I was only following orders....."
Posted By: WARREN1 Re: Don't look at me... - 04/17/02 07:25 PM
From the Designer's standpoint:
We never design a mistake into the project, intentionally. No one person is perfect, therefore, *&^%$$ happens on a project at some time.
Scenario #1- The owner of the facility should provide the contractor with adequate drawings or a well written and defined Scope of Work. If I were in the contracting business, that is what I would expect, otherwise, I would be very hesitant to take the job. Using the drawings or Scope to price the project, any errors would be brought to the attention of the owner. Resolutions and pricing adjustments via change order would follow.
Scenario #2- As a licensed electrician, any non-Code items on the drawings would stop the work for clarification using the proper channels. Any changes to the drawings based on the claifications would result in a change order. Bear in mind, ladies and gentlemen, you can make money on the change orders, if handled correctly. Again, the contractor should point out the errors during the bidding or pricing process, if called for on the drawings or specs.
For those who like to hammer the engineer- He went to college in electrical engineering, not National Electrical Code. Many are not licensed electricians, but licensed Professional Engineers, even though he should be very knoweledgeable about the Code. I'm not one of them, and have hammered them too, but like all professions, some are smart and others are a little less smart.
Whatever you do out there, be safe.
Posted By: The Watt Doctor Re: Don't look at me... - 04/17/02 10:24 PM
Mr. Warren,
Please accept my apologies for coming off harsh on EE's, GC's, A's, but if you'll notice I put a disclaimer in my post. [Linked Image]
"I have no intent of being offensive here..." The fact is, I have "muy respecticimo" for them all. The problem comes into play when, as Redsy so eloquently stated, someone says, "Don't look at me.... [Linked Image]." On top of that, what really "steams" me is that the spec's are written to "protect" the EE, and architect.
Little EC comes along, and thinks that he doesn't have a leg to stand on. I say he does. Spec's, contract language, etc, etc, etc can both help, and hurt everyone. Know where to draw the line in the sand, and stand your ground.

Sincerely, and Respectfully, but not angrily (this time),
Doc
Posted By: WARREN1 Re: Don't look at me... - 04/18/02 12:48 PM
No, Watt Doctor, I didn't think you were harsh on PE's. Not as hard as I am, sometimes. I work for a large engineering, procurement, and construction company, and with several PE's. As I stated, many don't have an electrician license and depend on underlings such as myself, and the contractors to catch the uh-ooh's. I do have a journeymans license, but don't know much about the "real" world of installation.
Our specs are not necessarily designed to protect anyone, just to get a good installation. Other specifiers may be different. Example: In our specs, we call for Nema 12 cabinets in certain areas, and Nema 1 gasketed in others. We also specify double lock-nuts, and Myers Scru-Tites. Now one would think that the contractor would know automatically which to use where. Well, that didn't happen on the last project. They put double lock-nuts on the Nema 12 cabinets in some places, and Meyers on the Nema 1's in some places. The Owner finally paid for the change, however, I never agreed then or now that he should have. The contractor is a large electrical contractor, supposedly well respected. And I can give you more examples of contractor and designer mistakes.
I have been watching this board for a while now, and have a great deal of respect for the posters here, including you, because they know more of the Code than I do.
With Much Respect, and work safe.
Posted By: Trainwire Re: Don't look at me... - 04/18/02 12:58 PM
Quick story, my father worked in prototype dept of a large electrical manufactureing Co.
(The first motion detector still turns his porch light on and off), and he got a schematic one time from the ol' EE dept. The 110 came in the cord, through the switch to the fuse and back out the cord. He never did tell me what the EE said when he showed it to him.
Trainwire
Posted By: sparky Re: Don't look at me... - 04/19/02 12:42 AM
To me, it's not the mistake per se'......... It's who'll own up to it......
Posted By: The Watt Doctor Re: Don't look at me... - 04/20/02 12:56 AM
If I may, please allow me to add alittle more color to my earlier statements. Part of my problem is that I have sat in on those meetings where the guy across the table says, "Well, you should have noticed that." Another common statement is, "Every electrician knows to look for that." I've also received phone calls (that the GC didn't know about because the architect didn't want them to know that he was calling me) that amounted to "unofficial" "official" directives that would have cost my company thousands of dollars. My responce is, if you are human enough to make the mistake, then I'm human enough to miss it during the bidding process.
Also, Warren, there was a typographical error in your first post that amounted to *&^%$$. What does that mean? [Linked Image]

#$!%**ologically Yours,
Doc
Posted By: motor-T Re: Don't look at me... - 04/20/02 01:49 PM
Warren:
Gotta take issue with this one. Drawings are never perfect but when an error is found it is the responsibility of the 'Designer'to make corrections. These drawings should always be checked, the checker should be well versed in all the aspects of the job, The places I worked for the checker was usually someone who had years and years of experience, and even he would miss an occasional mistake, When we estimated a drawing it would generally be 40 hours per drawing this included the engineering, the drawing the checking then to the draftsmen making the corrections then back to the checker for a final approval before going back to the engineer.
The Engineering firm has a responsibility too and should be accountable for its mistakes.
One project I worked on was a 150 foot Anneal and Pickle line the electrical part of it alone contained 250 drawings and this was not including the computer automation or the drives. From Conduit and cable schedules to the Red Conccrete, Took us 13 months to get the first draft of drawings out, ie made, checked and rechecked, and everytime the installations contractors found a mistake we had better make it right.
I dont know what the legal ramifications were but we were the Greenfield Designer. In that time period I spent more time on that job than I did with my family.
But it is my opinion that the Architect, Designer, Engineer is ultimately responsible and should be.
-Mark-
Posted By: sparky Re: Don't look at me... - 04/20/02 05:03 PM
Many moons ago, i did a decade in high tech, i worked with engineers & draftsmen on prototype material. It was a constant SNAFU, the only saving grace being that some interfaced better than others.
The same animal exists here, in the construction arena, so ask yourself how many times there had been a pre-bid meeting? Did the trades get together before the first hammer swing? ,was there a chance for exchange, Q&A, concerns?
I've worked the latter, as well as those jobs dictated without this benifit, the bottom line is,{scenario #1 & #2} you make the call, you take the fall.....
Posted By: Scott35 Re: Don't look at me... - 04/21/02 06:59 AM
Personally, I have seen both sides - the Designing / EE side and the Contracting / Bid / EC side. Each side has valid arguments as to whom is responsible.

For me, I would find it very uncomfortable to send out any bid sets which were not Engineered properly and WITH ENGINEERING ETHICS!!! [sorry to shout this, I'll explain why later].
My Prelim. E Sheets were - and will continue to be - complete in project scope / description, comply with applicable code[s] and conform to the client's specs. Also, I make the stuff "Electrician Logical" [circuit numbers in order, etc.] and properly size circuits for loads [200% grounded conductors where applicable, proper IG's, etc.].
This results in little - if no - Plancheck revisions to the preliminary bid set.
Same goes with sets that are revised as the project evolves [such as "SK"'s].

On the Bidding / EC side, one problem I am currently having is that I am no longer working "Semi-Solo", but now work for another General Contractor who does "Inhouse Electrical". Great Company to work for! Everyone is sharp, understands their work, etc.
For the 3rd time now I have been asked to bid projects [Bank Branch remodels / T.I.]. I have found each of the E sets to be a complete joke!!! The last set's E sheets look like they were 2/3 of the way finished before being sent to the Architects!
This set has some circuitry overkill, but very sloppy CAD and Engineer work runs rampant throughout the E sheets!!! Macros being used improperly, attributes not labeled correctly - or text wrapped bad [or over other text], Blocks pasted to the drawing to be copied, but left all over the place [in the wrong places!], etc., etc., etc...

The other 2 sets were just a joke! Covered only by disclaimers "Install per applicable codes" and "Install per client's specs". No scope, no existing plan, no nothing!

I'm currently working on a project in which the "Approved Planset" - the one stamped by the city, which has passed plancheck - had no 1 line diagram, no load schedules, nothing listed for AC units' branch circuit sizes or conduit sizes, nothing regarding subfeeds, 1/2 A** panel schedules, silly Title 24 energy conservation items, the typical Blocks used for teller line outlets [which have never been correct!], on and on!!!

To sum it up, NO ENGINEERING ETHICS!!!

As to Rojo-sy's scenarios, I could point out the following:

Scenario #1: The Contractor is at fault, since the Contractor is supposed to perform the Installation to any Applicable codes.
Since it has been accepted and paid for, the 1 year warrantee is binding the EC to any breakdowns of installed equipment.
--HOWEVER,--
Since the job has been accepted by the client, if there are any code issues, it's now the CLIENT'S responsibility to satisfy the Building Dept. This one could fall back into the 1 year warrantee [I suppose], so there's a good scenario for the lawyer to ponder.
To me it seems that the Client is now responsible to bring things up to code, but may take action against the EC for not complying to a contract. If the contract for some odd reason does not specify installing to code[s], or overseeing that codes are satisfied, that might place 100% burden on the Client.

Scenario #2: This one seems simple to me, but has been bounced around for days on a few projects [more than I would like to have seen!].
This one sure places the EC at fault, but the provisions of the prelim bids are to bid from the planset AS SHOWN. If any conflicts or inconsistency after project's beginning - which were unseen at the time of proposal by the EE or the EC, submit this to the EE / Architect [AKA Try to Request for Extra].

On almost every project I am involved with, the short and long term code issues are not something that would just "Pop Up". Can't say the same for other projects.

Scott SET