Posted By: maintenanceguy 570Volts? - 04/16/02 09:20 PM
Ordered a motor today through Grainger. Noticed several motors on the same page listed for 570Volts. I've just never seen a 570V service before. Where are they used, who has them?
Posted By: WARREN1 Re: 570Volts? - 04/16/02 09:28 PM
Typically, in the textile industry you will find the 600 volt systems.
Posted By: CTwireman Re: 570Volts? - 04/16/02 10:59 PM
They could possibly be for sale to Canada as well. They use 347/600 volt wye systems.
Posted By: Tom Re: 570Volts? - 04/17/02 12:06 AM
I've run across one system in 28 years & it was at a coal mine.
Posted By: Bjarney Re: 570Volts? - 04/17/02 01:12 AM
Maybe it's 575 volts. That's a standard nameplate rating for motors operating on 600V distribution--in the same way that 460V motors are intended for 480V systems {or 200V motors for 208V systems.}