service disconnect - 04/04/02 03:06 AM
200 amp service ,in a strip mall. service entance about 100 ft. from store, 200 amp disconnect under meter base . is their a requirement that that the service panel have a main breaker installed? and if not what would you do ? thank you .
because of the 100 ft. of entance conductors
i think i would use main in service panel.The real problem is this area if you dont like what inspector say you can call another not a good situation thank you very much.
[This message has been edited by kenrod3020 (edited 04-03-2002).]
thanks all for help. i would use main breaker in this install because i think the code in this area is the minimum standard .
if i get the job great if not, its ok
[This message has been edited by kenrod3020 (edited 04-06-2002).]
[This message has been edited by kenrod3020 (edited 04-06-2002).]
because of the 100 ft. of entance conductors
i think i would use main in service panel.The real problem is this area if you dont like what inspector say you can call another not a good situation thank you very much.
[This message has been edited by kenrod3020 (edited 04-03-2002).]
thanks all for help. i would use main breaker in this install because i think the code in this area is the minimum standard .
if i get the job great if not, its ok
[This message has been edited by kenrod3020 (edited 04-06-2002).]
[This message has been edited by kenrod3020 (edited 04-06-2002).]