ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Increasing demand factors in residential
by gfretwell - 03/28/24 12:43 AM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
Cordless Tools: The Obvious Question
by renosteinke - 03/14/24 08:05 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (Scott35), 262 guests, and 17 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#134914 12/06/02 11:10 PM
Joined: Dec 2000
Posts: 4,294
Member
I work with a couple of manufacturing companies that have home bases out of the US.
We've added 480x380,etc. transformers and odd buck/boost transformers (autotransformers) to spots as needed for the occasional odd voltage (here 277/480Y, 120/208Y are our nominal voltages).
I now have been "elected" to find a way to supply 100 volt power.
Does anyone have a source for this?
I only need about 30KVA, but I'm at a loss for the 100v 60Hz power, as the transformer doesn't seem to be available here in the US, and the manufacturer, in Japan, hasn't responded.
Thanks..S


[This message has been edited by electure (edited 12-07-2002).]

#134915 12/07/02 01:36 AM
Joined: Apr 2002
Posts: 2,527
B
Moderator
Must the 100 volts be one 2-wire circuit? At 30kVA, that is 300 amperes. Safely designed maybe, but not cheaply.

Could the 100-volt load be split into 3 parts? That could reduce material costs some.

What is the acceptable voltage range for the nominal 100-volt equipment? Is a ~104-volt nominal acceptable?





[This message has been edited by Bjarney (edited 12-07-2002).]

#134916 12/11/02 08:22 PM
Joined: Dec 2000
Posts: 4,294
Member
Yes, Bjarney, a voltage of 104 is acceptable, and a 3Ø system would be fine!
The circuits will be be used for industrial process equipment. We're supposed to install a few of the branch circuits now, and the bulk of the capacity is to be used for future expansion. (I've not even seenany of the equipment.)

[This message has been edited by electure (edited 12-11-2002).]

#134917 12/12/02 02:17 AM
Joined: Apr 2002
Posts: 2,527
B
Moderator
At http://www.federalpacific.com/literature/drytrans/FPTS-RTB-0701.pdf page 12, you could possibly use a 120:16V 5kVA {SB16N5F} transformer. that would buck 120V to 104V at 313 amperes. Else, if the “30kVA” feed was 4-wire wye, you could use three 2kVA {SB16N2F} transformers, each connected on a per-phase basis.

For 2-wire 120-to-104 volts connect 120V and 104V neutrals paralleled to H2/H4, with the 120V “hot” to H1/H3 and X1/X3, and 104V “hot” to X2/X4.

Use one 2kVA transformer for each 208Y/120V phase terminal.

#134918 12/20/02 11:07 PM
Joined: Dec 2000
Posts: 4,294
Member
Bjarney,
Thanks! I hadn't even thought about bucking this one down with autotransformers. Now they'll have their 104/180Y panel.
[Linked Image] Now what colors am I going to use for that one? (Only kidding, but heck I've about run out!)
Thx...S




[This message has been edited by electure (edited 12-20-2002).]

#134919 12/21/02 12:13 AM
Joined: Apr 2002
Posts: 2,527
B
Moderator
Been thinking about phase colors...how about puce, salmon and burnt sienna with a putty neutral?