OK- honest opinions here.....is this an adequate way to hang pipe? By using 'plumbing tape?' (Found this...not my work!)
- renosteinke
|
|
|
|
Joined: Mar 2005
Posts: 1,803
Member
|
Industrial location? Probably strong enough in direct tension, (apart from the dubious fix with a couple of clout nails), but there's no lateral restraint. Is this strap galvanised steel or plastic? The floor joists look on the thin side too. They look like floorboarding laid on edge! The risk here is joists 'rolling'. No herring-bone struts visible to counter this.
Alan
spelling
[This message has been edited by Alan Belson (edited 11-22-2005).]
Wood work but can't!
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
Honestly I have never done that. That aside I think we would be hard pressed to cite a legitimate violation here. We might say that... 358.6 Listing Requirements. EMT, factory elbows, and associated fittings shall be listed. ...requires the use of listed hangers but that means unistrut clips will be a violation as well. Bob
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
Joined: Jan 2005
Posts: 5,445 Likes: 3
Cat Servant Member
|
Alan- The location was a government office. Everything you see was concealed above a suspended ceiling. The wood joists are actually 2x12's (actual measure more like 1 1/2 x 10 1/2 inches) used as rafters to support the roof. To the right, you can just make out the solid wood blocking, used as lateral bracing between the rafters. It's not obvious in the pic, but there is a significant slope to these rafters. Let's just say that this "flat" roof has enough slope you don't need to worry about water forming puddles!
The "plumbers' tape" is galvanised steel, of a gauge just a little too heavy to be easily cut by your diagonal cutters, but easilt cut with aviation snips. (Maybe 18 gauge?)
|
|
|
|
Joined: Mar 2005
Posts: 1,803
Member
|
Rono; My apologies! My dopey old brain read that as one pic showing 2 floors at a landing! Duh! Lumber of those dimensions is not readily obtainable off the shelf at a builders' merchants in thr UK or Fr., I thought they were about 1x8 Alan
Wood work but can't!
|
|
|
|
Joined: Nov 2000
Posts: 2,148
Member
|
I really don't see that installation as any different from the use of 1/4" threaded rod and a mini. Don
Don(resqcapt19)
|
|
|
|
Joined: Feb 2005
Posts: 219
Member
|
Its "hack electrical work"!
Runs should be parallel and purpendicular to the building. The strapping is not legal in my area due to the quake zone I live in, but what moron would use that material to support any conduit run anyway. A good quake would take it out. Or, if you were working in that cieling, lost your balance, grabbed that run to balance yourself it would come down.
|
|
|
|
Joined: Oct 2004
Posts: 276
Member
|
adequate? probably.
workmanlike? no way.
|
|
|
|
Joined: Oct 2004
Posts: 276
Member
|
>>Or, if you were working in that cieling, lost your balance, grabbed that run to balance yourself it would come down.<<
I have seen 3/4 emt "batwinged" to ceiling wires before and thought that same thing...
|
|
|
|